Hot water heat: Can I use one powerful circulation pump to boost water flow of multiple zones?

Users who are viewing this thread

curious1

New Member
Messages
29
Reaction score
0
Points
1
Location
New York
We have hot water heat. We have three separate zones. Each zone has a separate pump that gets triggered by it's own thermostat. (No zone valves - just "zone pumps").

The hot water was not circulating quick enough through the radiators (which caused boiler shutoff etc). We added a second pump to each zone and it helped, but we want to add a third pump.

Could we add ONE pump in the main feed for ALL the zones (which is Cheaper/Less work/Less electricity)?

Or do we need to add a separate pump for each zone?
 
Last edited:

curious1

New Member
Messages
29
Reaction score
0
Points
1
Location
New York
(My initial concern with one pump was that when "zone 1" will turn on - this main pump will also pump hot water to "zone 2" and "zone 3".
One the other hand since only "zone 1" will have it's own pumps running - maybe those pumps will direct all the water to zone 1 and not allow any water into the other zones.

Which calculation is right??)
 

curious1

New Member
Messages
29
Reaction score
0
Points
1
Location
New York
Also adding a third pump to every single zone may pose a problem. There will be a total of 11 pumps. (9 + hot water + internal boiler pump). On a cold day when all pumps work together (85w x 11 =935 watts + boiler) it might overload the circuit breaker.)
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
There's a limit on how fast you can move water through a system for long-term reliability...too fast and it starts to make noise, could cause cavitation, and that can cause literal wear on the insides of the systems...wearing away the metal. Are there any valves in the system? If you have any partially closed, at restriction could cause imbalances. How many feet is it from the boiler location to the highest point? Are you sure you got all of the air out of the system? What pressure are you running? You need enough to ensure there is some pressure at the highest point...water column pressure will drop about 0.43#/foot of elevation change. Your pump needs to be able to overcome the head pressure, but the falling water on the return means it will flow if you can get it over the top...any air there will potentially stop it. Last, depending on the type of radiator...they could be quite corroded internally, and no amount of pressure will flow much through them. Same is possibly true if the pipes are iron and there has been any leaks...adding water means adding dissolved oxygen, which means rust, which means restrictions.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
Oh my. First off, one pump is sufficient and 99% of the time it will be plenty enough pump unless it's trying to move water up ten stories or so. Adding pumps is insanity, the radiators aren't heating then there's probably air in the system. Second, yes, the boiler shuts off. Again 99% of the time the boiler is oversized for the load so it will reach high limit and shut off the burner. The pump(s) should continue to run until the thermostat is satisfied. If they shut off when the burner shuts off, there is a wiring problem. Other zones will not overheat on a call from a single or even two other zones because there is supposed to be flow check valves installed on all of the zones.
 

curious1

New Member
Messages
29
Reaction score
0
Points
1
Location
New York
There's a limit on how fast you can move water through a system for long-term reliability...too fast and it starts to make noise, could cause cavitation, and that can cause literal wear on the insides of the systems...wearing away the metal. Are there any valves in the system? If you have any partially closed, at restriction could cause imbalances. How many feet is it from the boiler location to the highest point? Are you sure you got all of the air out of the system? What pressure are you running? You need enough to ensure there is some pressure at the highest point...water column pressure will drop about 0.43#/foot of elevation change. Your pump needs to be able to overcome the head pressure, but the falling water on the return means it will flow if you can get it over the top...any air there will potentially stop it. Last, depending on the type of radiator...they could be quite corroded internally, and no amount of pressure will flow much through them. Same is possibly true if the pipes are iron and there has been any leaks...adding water means adding dissolved oxygen, which means rust, which means restrictions.

Your answer (as well as Tom's) seems to show a lot of experience (and received a like).
What do you mean "What pressure are you running"?

-We are using 3/4 Pex (barrier) and new space saver radiators. It is possible that the pex fittings (which are smaller (1/2 inch)) along with all the twists and turns in the radiators contributed to the problem.

-The boiler kept on reaching high limit and shutting off (on each of the three zones including the basement). This happened only by the radiator heat, but did not happen when heating the water in the tankless water heater (which uses 1 inch copper)- so there is no problem with the boiler. The original licensed professional boiler specialist gave up on hope the non working system and blamed the ones who installed the radiators.

-The water is moving tooooo slow even with 2 pumps. I tried almost everything you said. Bleeding etc. The returning water was heating extremely slow. Finally adding a second pump to each zone helped a little. In addition we lowered the setting of the boiler and a few other things. This helps But still causes occasional boiler shutuff.

- Now I just added additional house space to be heated and more radiators to one zone and the two pumps are again not enough.


A-Based on your response There are still two things for me to try -
1- See if the check-valvles are adding too much restriction
2- Take a closer look at the flow rate of each zone - if one zone does better than others I will try to identify the cause.

B- Back to my non conventional idea of adding more pumps:
To make things even more complicated for a non experienced plumber: If 2 or more zones turn on together at once - the boiler does not overheat. This is probably because we have more water and pumps coming in.
This is why I want to know if I put 3 pumps on the main supply line and then just 1 pump on each zone, will the pump on each zone direct all the water from the previous 3 pumps to only go into it's zone and not the other zones?
 

curious1

New Member
Messages
29
Reaction score
0
Points
1
Location
New York
Oh my. First off, one pump is sufficient and 99% of the time it will be plenty enough pump unless it's trying to move water up ten stories or so. Adding pumps is insanity, the radiators aren't heating then there's probably air in the system. Second, yes, the boiler shuts off. Again 99% of the time the boiler is oversized for the load so it will reach high limit and shut off the burner. The pump(s) should continue to run until the thermostat is satisfied. If they shut off when the burner shuts off, there is a wiring problem. Other zones will not overheat on a call from a single or even two other zones because there is supposed to be flow check valves installed on all of the zones.

Your answer also shows to have a lot of experience in this field (and get a like). As I mentioned to jadnashua - the original licensed proffesional boiler expert gave up after 2 days of trying and blamed the plumber who did the piping.

We did lower the fire on the boiler, but lowering it only helped after we also added the pumps. Bleeding did not help. All three zones have the same identical problem. I will try desperately to find some restriction in the main supply line leading to the zones. Otherwise, if all fails, and I am left with no alternative, maybe you could advise on the idea of adding more pumps to the main supply line??
 
Last edited:

curious1

New Member
Messages
29
Reaction score
0
Points
1
Location
New York
P.S. I thought of an idea of taking all six pumps and lining them all up on the main supply line and using zone valves for the zones instead, but that will be a lot of work and plumbing. (Also that will reduce the main supply line to 3/4 and the water will rush very quickly through the line especially when all zones will work together).
 
Last edited: