JayOne23
Annapolis
I need help with a new thermostat i swapped out. The old thermostat (see attached photo) had a jumper between W & Y. The new thermostat which is the Honeywell touch RTS8500 series says it doesn’t require a jumper. The heat seems to work and the fan works but I’m not getting any cold air. Any help would be greatly appreciated. Thanks in advance
Fitter30
Peace valley missouri
How many wires and colors? Can't have a jumper between w & y .
W is heat
Y cooling
R is power
G is fan
W heat
C is common
R to G should turn on fan
R to W heat
R to Y cooling outside unit
Normal colors
R red
W white
G green
Y yellow
C black
Do not touch R to C
WorthFlorida
Solutions
Orlando, Florida
What type of system do you have? Pages 16,17, &18 of the installation manual. The orange wire (O terminal) is for Heat Pump operation and the the important setting is on page 17, function 0190. Most HP/AC units default to heat mode and power has to be applied to the O terminal so the reversing valve operates to places it in cool mode. There are some that are opposite. Power to the O lead to place the unit in HP mode. Your new thermostat this should be set to 0 since you get heat when you change the mode to cool.
Screen Shot 2022-11-04 at 7.31.34 PM.jpgScreen Shot 2022-11-04 at 7.32.05 PM.jpgScreen Shot 2022-11-04 at 7.32.43 PM.jpg