Hi everybody!
Can someone kindly look over these load calculations? This is my first time doing this and I'd like feedback.
Thanks!
Unit #1
220.12 General Lighting
220.42 Lighting Load Feeder Demand Factors
220.54 Electric Clothes Dryers
220.55 Electric Ranges--Dwelling Units
220.51 Largest of Fixed electric space heating loads or A/C load:
220.21 Non-coincident Loads
220.53 Appliance load--Dwelling Units
220.53 Appliance load--Dwelling Units (75% Total Appliance Demand Load) = 2,457.00 va
220.50 Motor Loads @ 120 Volts
TOTAL CALCULATED DEMAND LOAD in Volt-amperes = 34,215 va
TOTAL CALCULATED DEMAND LOAD in AMPS @ 1 Phase 3 Wire, 120/ 240 Volts = 143 Amps
MINIMUM SERVICE REQUIRED = 143 AMPS
SERVICE SIZE REQUEST = 150 Amps for Unit #1
Unit #2
220.12 General Lighting
220.42 Lighting Load Feeder Demand Factors
220.54 Electric Clothes Dryer
220.55 Electric Ranges--Dwelling Units
220.51 Largest of Fixed electric space heating loads or A/C load:
220.21 Non-coincident Loads
220.53 Appliance load--Dwelling Units
220.50 Motor Loads @ 120 Volts
Total Motor Demand Load = 945 va
TOTAL CALCULATED DEMAND LOAD in Volt-amperes = 29,734 va
TOTAL CALCULATED DEMAND LOAD in AMPS @ 1 Phase 3 Wire, 120/ 240 Volts = 124 Amps
MINIMUM SERVICE REQUIRED = 125 AMPS
SERVICE SIZE REQUEST = 125 Amps for Unit #2
These calculations are for two units in a building that has 200 amp service for the entire building. I asked for the electricity to be split between the two units. Initially, I requested two 125 amp panels to be installed in each unit (but instead got two 100 amp panels). However from these load calculations, I believe Unit #1 needs a 150 amp breaker panel, not 125 amp and Unit # 2 is ok with the 125 amps.
Should the electrician have done these 2 load calculations in order to determine the correct panel size for each unit? Am I correct that these calculations can be used to determine the units' panel size? Am I also correct that Units 1 & 2 require 150 amp & 125 amp panels, respectively?
Electricity's kinda fun...
Thanks for your help.
Cub
Can someone kindly look over these load calculations? This is my first time doing this and I'd like feedback.
Thanks!
Unit #1
220.12 General Lighting
3va/ft^2 of floor area, including unused space adaptable for future use
Floor Area= 1582 ft^2 = 4,746 va
220.52(A) Small Appliance LoadFloor Area= 1582 ft^2 = 4,746 va
1500 va for each 20 amp branch circuit required per 210.1(C)(1) in EACH kitchen, pantry, breakfast
room, dining room, or similar areas
# of Small Appliance Branch Circuits = 3 X 1500 va = 4,500 va
220.52(B) Laundry Load room, dining room, or similar areas
# of Small Appliance Branch Circuits = 3 X 1500 va = 4,500 va
# of Laundry Branch Circuits = 1 X 1500 va = 1,500 va
Total General Lighting & Appliance Load = 10,746 va220.42 Lighting Load Feeder Demand Factors
First 3000 or less at 100% = 3,000 va
From 3001 to 120,000 at 35% = 2,711 va
Remainder over 120,000 at 25% = 0 va
Total Lighting Demand Load = 5,711 vaFrom 3001 to 120,000 at 35% = 2,711 va
Remainder over 120,000 at 25% = 0 va
220.54 Electric Clothes Dryers
Dryer #1, Greater of Nameplate KW rating or 5kw = 7.20 kw = 7,200.00 w
220.55 Electric Ranges--Dwelling Units
Electric Range Nameplate KW = 10.00 kw = 10,000 w
220.51 Largest of Fixed electric space heating loads or A/C load:
220.21 Non-coincident Loads
Fixed Electric Space Heat #1 - w A/C#1 = 43.0 MCA@208-240V
Total Non-coincident Load = 7,632 va220.53 Appliance load--Dwelling Units
Qty Description va (watts)
1 Dishwasher(s) = 1200
1 Microwave(s) = 1100
1 Refrigerator(s) = 350
1 Rinnai Gas H2O Heater = 76
1 Stand Alone Ice Maker = 550
Total Connected Appliance Load = 3,276.00 va1 Dishwasher(s) = 1200
1 Microwave(s) = 1100
1 Refrigerator(s) = 350
1 Rinnai Gas H2O Heater = 76
1 Stand Alone Ice Maker = 550
220.53 Appliance load--Dwelling Units (75% Total Appliance Demand Load) = 2,457.00 va
220.50 Motor Loads @ 120 Volts
Qty Description Amps
1 Garbage Disposal(s) = 8.1
Total Motor Load = 972 va1 Garbage Disposal(s) = 8.1
430.24 25% of Largest Motor Load = 243 va
Total Motor Demand Load = 1,215 vaTOTAL CALCULATED DEMAND LOAD in Volt-amperes = 34,215 va
TOTAL CALCULATED DEMAND LOAD in AMPS @ 1 Phase 3 Wire, 120/ 240 Volts = 143 Amps
MINIMUM SERVICE REQUIRED = 143 AMPS
SERVICE SIZE REQUEST = 150 Amps for Unit #1
Unit #2
220.12 General Lighting
3va/ft^2 of floor area, including unused space adaptable for future use
Floor Area= 500 ft^2 = 1,500 va
220.52(A) Small Appliance LoadFloor Area= 500 ft^2 = 1,500 va
1500 va for each 20 amp branch circuit required per 210.1(C)(1) in EACH kitchen, pantry, breakfast
room, dining room, or similar areas
# of Small Appliance Branch Circuits = 2 X 1500 va = 3,000 va
220.52(B) Laundry Load room, dining room, or similar areas
# of Small Appliance Branch Circuits = 2 X 1500 va = 3,000 va
# of Laundry Branch Circuits = 1 X 1500va = 1,500 va
Total General Lighting & Appliance Load = 6,000 va220.42 Lighting Load Feeder Demand Factors
First 3000 or less at 100% 3,000 va
From 3001 to 120,000 at 35% = 1,050 va
Remainder over 120,000 at 25% = 0 va
Total Lighting Demand Load = 4,050 vaFrom 3001 to 120,000 at 35% = 1,050 va
Remainder over 120,000 at 25% = 0 va
220.54 Electric Clothes Dryer
Dryer #1, Greater of Nameplate KW rating or 5kw= 7.20 kw = 7,200 w
220.55 Electric Ranges--Dwelling Units
Electric Cooktop Nameplate KW= 2.00 kw = 2,000 w
220.51 Largest of Fixed electric space heating loads or A/C load:
220.21 Non-coincident Loads
Fixed Electric Space Heat #1 - w A/C#1 = 13.4 MCA@208-240V
Total Non-coincident Load = 3,216 va220.53 Appliance load--Dwelling Units
Qty Description va(watts) Qty Description va (watts)
1 Dishwasher(s) = 1100 w
1 Freezer(s) = 300 w
1 Microwave(s) = 1000 w
1 Refrigerator(s) = 350
1 ECO 11 Water Heater(s) = 13680 w (240v * 57a)
Total Connected Appliance Load = 16,430 va
220.53 Appliance load--Dwelling Units (75% Total Appliance Demand Load) = 12,323 va1 Dishwasher(s) = 1100 w
1 Freezer(s) = 300 w
1 Microwave(s) = 1000 w
1 Refrigerator(s) = 350
1 ECO 11 Water Heater(s) = 13680 w (240v * 57a)
Total Connected Appliance Load = 16,430 va
220.50 Motor Loads @ 120 Volts
Qty Description Amps Qty Description Amps
1 Garbage Disposal(s) 6.3
Total Motor Load = 756 va
430.24 25% of Largest Motor Load = 189 va1 Garbage Disposal(s) 6.3
Total Motor Load = 756 va
Total Motor Demand Load = 945 va
TOTAL CALCULATED DEMAND LOAD in Volt-amperes = 29,734 va
TOTAL CALCULATED DEMAND LOAD in AMPS @ 1 Phase 3 Wire, 120/ 240 Volts = 124 Amps
MINIMUM SERVICE REQUIRED = 125 AMPS
SERVICE SIZE REQUEST = 125 Amps for Unit #2
These calculations are for two units in a building that has 200 amp service for the entire building. I asked for the electricity to be split between the two units. Initially, I requested two 125 amp panels to be installed in each unit (but instead got two 100 amp panels). However from these load calculations, I believe Unit #1 needs a 150 amp breaker panel, not 125 amp and Unit # 2 is ok with the 125 amps.
Should the electrician have done these 2 load calculations in order to determine the correct panel size for each unit? Am I correct that these calculations can be used to determine the units' panel size? Am I also correct that Units 1 & 2 require 150 amp & 125 amp panels, respectively?
Electricity's kinda fun...
Thanks for your help.