handyandy2
New Member
I've spent the entire past 3 days trying to diagnose the root cause of blowing slow-blow fuses. Follow along:
Fuses are blowing NOT due to amperage overload, but due to heat (suspected, as there is no definitive way to discern). There is no amp spike.....EVER.
What is working, and in spec are:
What say ye?
Fuses are blowing NOT due to amperage overload, but due to heat (suspected, as there is no definitive way to discern). There is no amp spike.....EVER.
What is working, and in spec are:
- 10kw heat strip blows hot, but will run for perhaps 20 mins, then blow a fuse
- Critical to know is the slow blow fuse box in the attic heats up the terminals (1 in particular)
- Since I have been watching the temp with a thermal gun, I shut the system down at 115d.
- It takes perhaps 10 mins to gradually reach 115d.
- Heat strip specs out with both ohm and volts (21amp, 240 volt, 11 ohm) - there are two
- Thermal limiters on heat strip are new (and test out ok)
- Total amp draw on circuit is 43 amps (60 amp fuses/box) 2 amps are the fan.
- No amp spike during operation, either during warmup or at full heat
- When one heat strip is disconnected, the amps drop accordingly, BUT the fuse box terminal continues to heat up.
- Sequencer is new, and checks out, and does allow one side to kick in first, then the other.
- Fan motor and cap is not an issue
What say ye?