Heater does not kick in after replacing heat exchanger

Users who are viewing this thread

GG_Mass

Member
Messages
105
Reaction score
2
Points
18
Location
Massachusetts
Hi everyone

I replaced the external heat exchanger on our hydronic system, after bringing everything back into pressure, the heating cycle starts briefly, and then the boiler shuts off, and a slight clicking sound emits from the "Taco Cartridge Circulator" .
Any ideas about what could be the reason ?

Thank you,
 
Last edited by a moderator:

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
Was it working before you replaced the heat exchange?
Who did the job?
 

GG_Mass

Member
Messages
105
Reaction score
2
Points
18
Location
Massachusetts
Was it working before you replaced the heat exchange?
Who did the job?
Yes, it was working before.

I did the job myself.

I found the issue - it was one valve in the loop that I mistook for a quarter-turn valve. It as a full spin valve. Once turning (opening) that valve to full-open, hot water started circulating again and the heater started working properly.

Thank you.
 