I'm running power from a GFCI outlet to two lights with a light
switch on the end of the power run using 12/2 wire. I have made a diagram giving the details (see link below).
1. Is this a correct configuration?
2. Will the lights and switch be protected by the GFCI (assuming I wire the GFCI correctly?

GFCI diagram.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
If you run the leads to the switch and lamps from the load side of the gfci, yes. Normally you'd continue the black to the switch and then designate the white as the switched lead with some red tape on each end.
 

Frenchie

Jack of all trades
Messages
1,239
Reaction score
0
Points
36
Location
Brooklyn, NY and Fire Island, NY
If you run the leads to the switch and lamps from the load side of the gfci, yes. Normally you'd continue the black to the switch and then designate the white as the switched lead with some red tape on each end.

Nope, he has it right.

The re-designated white should be the constant hot wire, the already-black wire is the switched.

I don't know why, and I'd have to dig a bit for the threads, but all the sparkies agree on it. It struck me as counter-intuitive, too, but that's the industry standard, apparently...


okay, I didn't have to dig that far:

http://forums.jlconline.com/forums/showthread.php?t=38064&highlight=3-way*

Apparently it's a code violation to do it otherwise.



*Standard JLConline link disclaimer: it's a pro-only site, and some people there can get pretty rude about it. If you're not an industry pro, you can read as much as you want, you can even register (allows you to download attachments, and saves you having to type a verification code when you search), but DO NOT POST there. Nobody will answer you, and they'll pick on you, as well. Exceptions to this rule: the electrical sub-forum, and the building-science sub-forum, are open to anyone.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks