Ideally that question would have been asked BEFORE the framing went up.
Assuming those are 2x4s (?), a
IRC code minimum for fully conditioned residential space in zone 4A is 2x4/R13 + R5 continuous insulation. With the intense summertime humidity and high moisture reservoir nature of brick cladding it's really good to have a vapor retarder between the outdoors and the air conditioned indoors to keep mold from growing on the cavity side of the wallboard from the high moisture content air.
If there is something like an inch of space between the stud maybe there's room to knock out a few studs and slip foil-faced rigid polyiso foam board (R6) there, fastening it tight to the CMU wall with a few cap screws. With polyiso it's good to stop an inch from the slab to avoid wicking up any moisture from the concrete, even if the concrete normally looks dry. Tape the seams of the polyiso with foil HVAC tape, seal the top & bottom edge of the foam board to the CMU with can foam or polyurethane caulk. This is a
lot easier do do
before the framing goes up.
If the gap is deeper than that, use thicker foam. 1.5" thick foil or plastic faced Type-I EPS would also run about R6, and is pretty cheap (even at box stores) and doesn't have the same moisture wicking issues of polyiso. Make it as snug a fit as possible, to allow reasonable fit for the cavity insulation.
Then, install batt insulation in the stud bays snugged up tight to the foam. Kraft faced is fine if that's any easier or cheaper, or unfaced. If fire resilience is a priority, unfaced rock wool batts would be best (but definitely not the cheapest.)
Foil facers are true vapor barriers, and will not allow moisture to pass through the assembly via vapor diffusion, so there should NOT be any true vapor barriers on the interior side or you'll have created a moisture trap. The foil facers will block the intense bursts of moisture loads that occur when the sun hits rain or dew wetted brick from reaching the cavities, and there is huge dew point margin against wintertime moisture accumulation at the foam/fiber insulation boundary- moisture won't accumulate to problematic levels over the winter when using only kraft facers or standard interior latex on wallboard as the interior side vapor retarder.
Most brick cladding on CMU walls have a 3/4"-1" cavity as a capillary break between the brick & CMU to keep moisture from wicking toward the interior. If your's doesn't have that gap installing fiber insulation in direct contact with the CMU without some sort capillary break is a disaster. But fiber insulation still needs an exterior side air barrier to perform to specification, so it might as well be R5 (or higher) foam board.