Hello everyone, I'm looking to install a hot tub. But before I do I want to make sure I have the correct voltage at my subpanel. The hot tub is 240v.
The subpanel runs off a double 60amp breaker from the main panel,which makes me think I'm ok but I'm not totally sure.
Any advice would be appreciated!

20190814_132423.jpg

20190814_135832.jpg
 

Reach4

Well-Known Member
Messages
38,863
Reaction score
4,430
Points
113
Location
IL
If that neutral is #4 AWG, you appear to be OK.

You will need to install a 60 amp 2-pole breaker for the 240 circuit. That is probably what you had in mind, but don't just call it a double breaker.
 