American Standard furnace freedom 90. 1 stage.
Furnace is intermittent. Code 3 pressure issue.
Tested with manometer getting 1.5wc, switch is rated 1.15wc
Ive narrowed it down to this
If I take the black tube off top of pressure switch that goes to gas valve and burner box everything works
if I open burner chamber everything works.
If I remove fresh air pipe everything works
I vacuumed and snaked the fresh air pipe.
Furnace is 10 years old.
Am I supposed to have equalized pressure in the burner box?