Extending Sewer Line for Toilet - Plumbing Configuration

Users who are viewing this thread

Gregj107

New Member
Messages
13
Reaction score
1
Points
3
Location
Montana
I am moving the toilet in my bathroom to an opposite wall and will need to extend the 3" sewer line about 9ft. The original toilet is at the end of the sewer line which will be removed. I would then use a 90 degree long sweep to connect the two sewer lines. I am using the UPC code.

In the diagram below does the plumbing look correct for the toilet? Also does the 2" vent line for the toilet need to go straight up to the attic or can it have a 90 degree in it? I do have a 1.5" vanity vent line about five feet from the toilet, wondering if I could change it to a 2" and have the toilet vent line connect into it instead running a separate vent line?

I appreciate the help as don't have any plumber close to where I live.

gregj107-01.jpg
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
The vanity if run with 2" could wet vent the toilet.
Also the two vents can combine at 42" or higher.

gregj107-01.jpg


Vertical to horizontal should be wyes and combo fittings.

index.php
 
Last edited:

Gregj107

New Member
Messages
13
Reaction score
1
Points
3
Location
Montana
Should the sanitary T in the picture for the vent pipe also be a wye combo? Last are these pictures of a combo and a wye/combo? Thank you

611942034642.jpg
611942035625.jpg
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,845
Points
113
Location
Berkeley, CA
A WC is the rare fixture where the vent takeoff could be a combo in that orientation. But a sanitary tee is fine and a combo has no advantage.

For any non-siphoning trapped fixture, for a vent takeoff while the drain turns down, a sanitary tee is mandatory and a combo is prohibited.

Cheers, Wayne
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
A toilet can go horizontally into a santee or a wye fitting but not vertical into a santee on it's back. The pop spreads out both directions. It needs a fitting that directs it downstream.

dwv_b2.jpg
 
Last edited:

wwhitney

In the Trades
Messages
6,567
Reaction score
1,845
Points
113
Location
Berkeley, CA
FWIW, I interpreted the last question to be about the upper 3" san-tee where the vent comes off. As Terry says, the lower 3" san-tee in the drawing needs to be a combo.

Cheers, Wayne
 