Electric Hot water tank Tripping daily

Users who are viewing this thread

Phog

Active Member
Messages
454
Reaction score
84
Points
28
Location
Rochester NY
The branch circuit. Is the new water heater the same power rating as the old one it replaced was? Ensure sufficient wire gauge & breaker size. Perhaps also switch the breaker with an adjacent one of the same current rating, to see if the breaker itself is functioning properly.

It could also be a short somewhere in the water heater internal wiring, for example where a wire is pinched. (Usually you will also see signs of this, such as shiny/melted or scorched wire insulation).
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,435
Points
113
Location
IL
You could throw your clamp-around ammeter on one of the hots, and compare the current to the breaker marking.

Daily seems to imply it can take a long time for the trip to happen.

One other thing: when the WH is cold, the top element will come on first. Then when the top is hot, the bottom one will come on.

A problem downstream of the top thermostat could cause a delay in the current rise on startup.
 