DWV Revised need input

Users who are viewing this thread

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
410CE436-5DD8-4B1A-AEFA-C3EEB4BDABAC.jpeg
1st floor bathroom, wide open from basement to 1st level roof. 1890’s farm house. Very small 5 1/2 x 5 1/2. Sorry for my 2nd grade drawing. Bathroom to have wall hung toilet, shower, and sink. So far here’s my plan. The second long sweep 90 is to get under the floor joist. I plan to tie in to the original horizontal drain line near the floor. The original stack minus the vent is still there just on the diagonal corner from the new toilet location. Any advice greatly appreciated. I haven’t figured out shower drain situation yet but considered utilizing the original stack and if necessary running another 2 inch vent up and tying in before through the roof.
 

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
View attachment 73099 1st floor bathroom, wide open from basement to 1st level roof. 1890’s farm house. Very small 5 1/2 x 5 1/2. Sorry for my 2nd grade drawing. Bathroom to have wall hung toilet, shower, and sink. So far here’s my plan. The second long sweep 90 is to get under the floor joist. I plan to tie in to the original horizontal drain line near the floor. The original stack minus the vent is still there just on the diagonal corner from the new toilet location. Any advice greatly appreciated. I haven’t figured out shower drain situation yet but considered utilizing the original stack and if necessary running another 2 inch vent up and tying in before through the roof.
 

Attachments

  • A7808B69-3054-43E1-B648-9E44308A7D20.jpeg
    A7808B69-3054-43E1-B648-9E44308A7D20.jpeg
    111.3 KB · Views: 112
  • 695DBA7C-CD25-4747-81C0-145E2056A0BC.jpeg
    695DBA7C-CD25-4747-81C0-145E2056A0BC.jpeg
    108.9 KB · Views: 131

wwhitney

In the Trades
Messages
6,559
Reaction score
1,842
Points
113
Location
Berkeley, CA
The collection of fittings in the upper right corner of your first photo, it's hard to tell what they are. Are any other drains coming into area, or can you just remove all of those and use the vertical drain for just the 3 bathroom fixtures? If other drains are coming in, we'd need to know about those and get a close up picture of what's going on there.

On a floor plan (or the last photo), how about drawing the locations of the in-wall toilet drain connection, the lavatory, and the shower and drain?

The connectivity in your drawing looks OK, but obviously you need to add the shower in. And that's an awful lot of 90 degree bends, hopefully there's a solution that would use fewer or change some to 45 degree bends.

Cheers, Wayne
 

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
image.jpg
image.jpg
image.jpg
Ok, I still am a poor artist. I’ve done a 3 wall drawing with 3 images starting at the beginning. View is from facing wall 1. Area is basically box shape.
Wall 1. Starting at shower with a 3 inch pipe and adding a 3 3 2 wye to pick up the shower drain. Next is a long sweep 90 to turn the corner. I picked the long sweep 90 vs just a 90 as I thought less prone to clogs. Onto wall 2.

Wall 2 picking up with that 90, the 3 inch pipe the adds a 3 3 2 wye for a 2 inch vent up and through the roof. Next the 3 inch line picks up the toilet with a 3 3 3 San T, before entering a long sweep 90 (turning the corner) to get to wall 3.
Wall 3 runs 3 inch to a 3 3 1.5 to pick up the sink. The sink drain enters the 3 inch pipe straight on with a reducer bushing 3 to 1.5. The 1.5 also serves as the sink vent up and out through the roof. Below the 3 inch pipe goes straight down and out the drain line.
Hope this makes sense.
 

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
Good grief. It’s been a long time since I did a remodel but looking at this this looks fairly stupid. Now I think I should just reconfigure the original stack in the corner to accept the sink, shower and toilet and vent accordingly
 

wwhitney

In the Trades
Messages
6,559
Reaction score
1,842
Points
113
Location
Berkeley, CA
Yes, starting fresh sounds like a good idea. So how about a floor plan (not an elevation) showing the fixtures, the drain below you need to tie into, and the location of any existing vents above that you can make use of?

Cheers, Wayne
 

Tuttles Revenge

In the Trades
Messages
4,178
Reaction score
1,440
Points
113
Looks like you have the room in that tiny crawler to put the plumbing anywhere you want. Draw your best layout for the bathroom design that you want and work to that goal. Anything is possible.. just time and money.
 

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
image.jpg
image.jpg
Here’s the layout. I have so far 2 vents, as shown. The old stack was to the top left. The vent pipe was in the room, and with space at a premium, I removed it to just under the floor. It went straight down then horizontal toward the bottom left of layout. That portion remains as is shown. Perhaps I can just use the old stack with my current vents? Stack appears to accept the 3 from toilet the 2 inch drain from shower and 1 1/2 for the sink? Not sure what to do with the top area where the vent was removed? Can it be capped if it’s deemed usable? Thanks for the help, as you can see I need it, as well as a redo of how to draw
image.jpg
image.jpg
 

Tuttles Revenge

In the Trades
Messages
4,178
Reaction score
1,440
Points
113
What is the walking distance between your toilet and the sink? That seems kinda narrow to me without knowing your overall dimensions. Is there room to put the sink and toilet on the same wall?

If it were me.. I think I would place the toilet between the sink and the shower. That is how I see most bathrooms designed.
 

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
This bathroom is very small. Width is 69” total x 7’2 Wall hung toilet projects 20”, and sink only projects 12”, approx 3 feet between front of toilet to sink edge. The placement was basically decided once the room was demolished. Built in 1890 and somebody made a mess over the years by removing several load bearing studs. I had to replace the floor joists as well as they’d chopped them up to near nothing. The shower will be at the back, approx 34 deep by 69 wide. The window is being moved and replaced with an awning window. Can’t have part of a window in the shower. I did extend the room a bit see pic below, also going with a pocket door to save space
 

Attachments

  • image.jpg
    image.jpg
    117.3 KB · Views: 122
Last edited:

Tuttles Revenge

In the Trades
Messages
4,178
Reaction score
1,440
Points
113
Right on! Looks like the toilet carrier fitting next to the shoes. Make sure the frame of the carrier is FLUSH with the rough wall surface or the toilet will smoosh through the finished wall whatever gap there is. What carrier / toilet combo are you using?
 

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
5FF4790A-3CFA-4908-B900-EBC13BCB2625.jpeg
Right on! Looks like the toilet carrier fitting next to the shoes. Make sure the frame of the carrier is FLUSH with the rough wall surface or the toilet will smoosh through the finished wall whatever gap there is. What carrier / toilet combo are you using?

Brand is FineFixtures complete combo. I think they’re outta Europe. Had great reviews and just have to figure out the height. I replaced and doubled up the wall, true 2x4’s, but the mounting bolts are now too short so going with lag bolts. The Wedi shower kit is on the way, heated floor, components for a lighted niche, but lots more to do. I decided to just use original stack as I don’t know wtf I was thinking, got fittings all over the place. I capped the top of the unused stack vent using a 5.5 inch. Fernco cap. I think I’m ok to glue up a few fittings. The new 2 inch vent will be shared by the toilet and shower with the sink drain on its own 1.5 vent tying into the 2 in the roof area.
 

Tuttles Revenge

In the Trades
Messages
4,178
Reaction score
1,440
Points
113
Looks good. Looks like most carrier manufactures have moved cross bars behind where the toilet will cantilever and crush through the finished wall now, so you're good on that aspect. I would mount the toilet to the frame before you sheetrock to test if or how it bounces. After the sheetrock crushing behind the toilet, a bouncing carrier is the biggest complaint I've experienced. That old growth should be super sturdy tho!
 

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
Looks good. Looks like most carrier manufactures have moved cross bars behind where the toilet will cantilever and crush through the finished wall now, so you're good on that aspect. I would mount the toilet to the frame before you sheetrock to test if or how it bounces. After the sheetrock crushing behind the toilet, a bouncing carrier is the biggest complaint I've experienced. That old growth should be super sturdy tho!
Thank you I will definitely do that. I think you’re right on the old growth. The farm carpenters had no issues removing lots of load bearing studs, sometimes 2 in a row. Seems this house was floating. I’m not surprised as 20 years ago I went to replace upstairs toilet and noticed a doubled joist cut all the way through. Did some investigating and they cut out both joists, on both sides to apparently fit plumbing on one end and duct work on the other. That forced the remodel. I forgot 1 question. Can the shower drain share the 2 inch vent which exists on the 3 inch toilet line?
 

Tuttles Revenge

In the Trades
Messages
4,178
Reaction score
1,440
Points
113
No drains can use another fixtures vent unless its properly wet vented. The original fitting you have, those are all drains entering horizontally and the toilets vent is taken off the top of where the drains enter it. The other branches would need to be vented indvidually.

Tho I suppose that fitting would work in a horizontal wet venting system as long as trap arm lengths are maintained. Not sure what code you're under, but the UPC (except for washington state) require the toilet to the the most downstream fixture (some dumb idea that you need other fixtures upstream to help wash down waste) in which you could argue that fixture complies with that.
 

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
Thank you. I will add another vent off the shower. I don’t suppose there’s a way to add back in a 2 inch vent from the top of the original stack? It had a 3 inch pipe vent but it was in the room. See pic, I put a fernco cap on
image.jpg
 

Casman

Member
Messages
130
Reaction score
3
Points
18
Location
New York
image.jpg
image.jpg
image.jpg

I think I have a new idea, if I put a fernco donut on the top of that stack, with a short 3 to 2 reducer, then I can 45 to get inside the wall then up. This would serve as the vent for the shower?

The top pic is the sink drain w/ vent, the in wall toilet with 2 inch vent then vent the shower near the top left where the original 3 inch vent was.
 