    Question for the pro's will this config work properly?
    Thank you.
    John
     
  2. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    The photo and the picture don't seem to match.

    To me, a Washington State plumber, it's not right for inspection.
    The toilet needs to be vented within six feet. A kitchen sink can't be used to vent it.
    A lav can, if you are running 2" for the lav and vent, within six feet. Once other waste is coming down the line, it's no longer a vent. I say that noticing that the lav is on the other side of a 3" main waste line.

    If that 3" near the toilet is truly a vent, you could throw a santee off the vertical and trap over with a 90.
    If there is plumbing coming down the stack, then that wouldn't work. Without seeing a drawing going through the roof, it's a bit hard knowing what the plan is.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. accidentalplumber

    accidentalplumber New Member

    Joined:
    Dec 19, 2012
    Location:
    Issaquah,Wa
    Hello Terry
    Thank you for the reply. I will try to make this less confusing. The vertical closest to the camera, just over the level will be the vent stack and will only have a tub and washer empty into it. It will also vent the basin. As far as the future toilet goes it will have its own vent when the time comes. Hope you are not totally confused now.
     
  5. accidentalplumber

    accidentalplumber New Member

    Joined:
    Dec 19, 2012
    Location:
    Issaquah,Wa
Similar Threads: configuration analysis
Forum Title Date
Plumbing Forum, Professional & DIY Advice Is this drain configuration acceptable? Oct 21, 2017
Plumbing Forum, Professional & DIY Advice Unusual Shower Valve Configuration Oct 2, 2017
Plumbing Forum, Professional & DIY Advice Kitchen Sink configuration May 30, 2017
Plumbing Forum, Professional & DIY Advice Which PVC configuration should I use? Apr 20, 2017
Plumbing Forum, Professional & DIY Advice Storage Tank and Pressure booster with tank configuration Mar 24, 2017

Share This Page