n the attached image, does this plumbing for a new double vanity look correct? Any possible UPC Permit problems?

dblvanity-plumbing.jpg
 

Reach4

Well-Known Member
Messages
38,882
Reaction score
4,433
Points
113
Location
IL
Not correct. Not correct UPC. Not correct IPC. The two trap arms are not vented..

Is that line from above a vent, or is it carrying drainage from the floor above?

One rework method is to replace the double wye with a double fixture fitting if the vent is good.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
Thank you for all the info! I replaced the wye with a double fixture. I should have known that, just stupid!

It's why we have the forums, so that we all can learn and the reasons for doing things. The more mistakes I have made the more I have learned.
I come up with an idea, I try it, discard it, next!!
One of my first jobs was in bicycle shops as a mechanic. Once day a customer asked why I wasn't loosening a certain screw on the front derailleur and I could not give him a good answer. I tried it and it was better than what I had been doing. You never know where the lesson will be coming from. It's my idea now.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks