To clarify, like in terms of the wye's configuration, but not in terms of what is upstream of the wye's branch. For a proper dry vent, the wye's branch needs to continue to under the wall, where it hits a 60 degree elbow to turn straight up.

Cheers, Wayne
So after running around several big box stores and plumbing supply houses, here's my mockup on the right. The left shows the WC and the mainline connection.

It looks like I need to dig down several inches more for the shower drain to make the mainline connection. I also need to extend my dry vent arm to go under that bottom plate where I'll drill a hole and go up and make the connection to my existing dry vent line from the lav.

What do you think?

20220204_092320.jpg
 

wwhitney

In the Trades
Messages
6,556
Reaction score
1,841
Points
113
Location
Berkeley, CA
Looks good.

I think you got a 45 and a 22.5 rather than a 60? That will result in rolling your wye less than 45 degrees, which is not optimal but should work, and will rise a bit slower making it easier to get the vent under the wall before it rises out of the slab. If you want to roll the wye a full 45 degrees, by trial and error you can get a net 60 degrees out of a 45 and a 22.5 by playing with the two joints (the one to the rising vent, and the one between the elbows).

Likewise, you have your trap in a flat P configuration. You can rotate the u-bend around your (not yet installed) drain riser, and rotate the elbow/u-bend joint, to get your shower drain to start closer/farther from the wall as required.

Cheers, Wayne
 

Dan Park

Member
Messages
41
Reaction score
2
Points
8
Location
Los Angeles, CA
Looks good.

I think you got a 45 and a 22.5 rather than a 60? That will result in rolling your wye less than 45 degrees, which is not optimal but should work, and will rise a bit slower making it easier to get the vent under the wall before it rises out of the slab. If you want to roll the wye a full 45 degrees, by trial and error you can get a net 60 degrees out of a 45 and a 22.5 by playing with the two joints (the one to the rising vent, and the one between the elbows).

Likewise, you have your trap in a flat P configuration. You can rotate the u-bend around your (not yet installed) drain riser, and rotate the elbow/u-bend joint, to get your shower drain to start closer/farther from the wall as required.

Cheers, Wayne
Thanks Wayne, I will definitely be playing around with all the angles!

I've just spent a few hours digging through this hard clay soil and jackhammering out part of the footing for the shower's dry vent. Ugh!!!

I should have some better pics tomorrow with the final install
 