dylannic
New Member
Just wondering what options I have for a T&P discharge location. The building is not done but will be a slab on grade single story house with septic tank. The utility room with water heater, pressure tank and small hydronic system is located at the back and only accessible from the exterior. Code does not directly dictate if it can or can't be discharged through a wall, I am in Atlantic Canada zone 6a so we have cold winters. Anyway, if anyone has any suggestions, I'd like to get away from having a floor drain if that's even possible with slab on grade and septic, I would prefer to have it go out the wall or other options and suggestions would be appreciated.
"2.6.1.7. Relief Valves"
1) In addition to the requirements in Sentence (2), the hot water tank of a
storage-type service water heater shall be equipped with a pressure-relief valve
a) designed to open when the water pressure in the tank reaches the rated
working pressure of the tank, and
b) so located that the pressure in the tank shall not exceed the pressure at the
relief valve by more than 35 kPa under any condition of flow within the
distribution system.
2) The hot water tank of a storage-type service water heater shall be equipped with a
temperature-relief valve with a temperature-sensing element
a) located within the top 150 mm of the tank, and
b) designed to open and discharge sufficient water from the tank to keep
the temperature of the water in the tank from exceeding 99°C under all
operating conditions.
3) A pressure-relief valve and temperature-relief valve may be combined where
Sentences (1) and (2) are complied with.
4) Indirect service water heaters shall be equipped with
a) a pressure-relief valve, and
b) a temperature-relief valve on every storage tank that forms part of the
system.
5) Pipes that convey water from a temperature-relief, pressure-relief or combined
temperature- and pressure-relief valve shall
a) be of a nominal pipe size at least equal to the NPS of the outlet of the valve,
b) be rigid, slope downward from the valve, and terminate with an indirect
connection above a floor drain, sump, or other safe location, with an air break
of not more than 300 mm,
c) have no thread at their outlet, and
d) be capable of operating at a temperature of not less than 99°C.
(See Note A-2.6.1.7.(5).)
6) The temperature-relief valve required in Clause (4)(b) shall
a) have a temperature-sensing element located within the top 150 mm of the
tank, and
b) be designed to open and discharge sufficient water to keep the temperature
of the water in the tank from exceeding 99°C under all operating conditions.
7) No shut-off valve shall be installed on the pipe between any tank and the relief
valves or on the discharge lines from such relief valves.
8) A vacuum-relief valve shall be installed when any tank may be subject to
back-siphonage.
9) Storage-type service water heaters that are located in a ceiling or roof space, or over
a floor of wood construction, shall be installed within a corrosion-resistant watertight
drain pan, as described in Sentence (10).
10) The drain pan referred to in Sentence (9) shall
a) be not less than 50 mm larger than the tank and have side walls not less
than 25 mm high,
b) be drained by a pipe two NPS larger than the relief valve discharge pipe, and
c) have a drain that is located directly under the relief valve discharge pipe
"2.6.1.7. Relief Valves"
1) In addition to the requirements in Sentence (2), the hot water tank of a
storage-type service water heater shall be equipped with a pressure-relief valve
a) designed to open when the water pressure in the tank reaches the rated
working pressure of the tank, and
b) so located that the pressure in the tank shall not exceed the pressure at the
relief valve by more than 35 kPa under any condition of flow within the
distribution system.
2) The hot water tank of a storage-type service water heater shall be equipped with a
temperature-relief valve with a temperature-sensing element
a) located within the top 150 mm of the tank, and
b) designed to open and discharge sufficient water from the tank to keep
the temperature of the water in the tank from exceeding 99°C under all
operating conditions.
3) A pressure-relief valve and temperature-relief valve may be combined where
Sentences (1) and (2) are complied with.
4) Indirect service water heaters shall be equipped with
a) a pressure-relief valve, and
b) a temperature-relief valve on every storage tank that forms part of the
system.
5) Pipes that convey water from a temperature-relief, pressure-relief or combined
temperature- and pressure-relief valve shall
a) be of a nominal pipe size at least equal to the NPS of the outlet of the valve,
b) be rigid, slope downward from the valve, and terminate with an indirect
connection above a floor drain, sump, or other safe location, with an air break
of not more than 300 mm,
c) have no thread at their outlet, and
d) be capable of operating at a temperature of not less than 99°C.
(See Note A-2.6.1.7.(5).)
6) The temperature-relief valve required in Clause (4)(b) shall
a) have a temperature-sensing element located within the top 150 mm of the
tank, and
b) be designed to open and discharge sufficient water to keep the temperature
of the water in the tank from exceeding 99°C under all operating conditions.
7) No shut-off valve shall be installed on the pipe between any tank and the relief
valves or on the discharge lines from such relief valves.
8) A vacuum-relief valve shall be installed when any tank may be subject to
back-siphonage.
9) Storage-type service water heaters that are located in a ceiling or roof space, or over
a floor of wood construction, shall be installed within a corrosion-resistant watertight
drain pan, as described in Sentence (10).
10) The drain pan referred to in Sentence (9) shall
a) be not less than 50 mm larger than the tank and have side walls not less
than 25 mm high,
b) be drained by a pipe two NPS larger than the relief valve discharge pipe, and
c) have a drain that is located directly under the relief valve discharge pipe