Cutting old galvanized to couple to new brass or PVC P trap. Nervous.

Users who are viewing this thread

Jeff H Young

In the Trades
Messages
8,766
Reaction score
2,168
Points
113
Location
92346
Don't worry it might not have broke . hopefully you can use a cut off wheel get nice clean cut after you break out concrete
 

Modulerics

Member
Messages
31
Reaction score
1
Points
8
Location
New Jersey
Alright. After a 45 it looks like more galvanized that's then leaded into a cast iron hub. Thoughts?

20221024_143933_copy_1612x1209.jpg
 

Jeff H Young

In the Trades
Messages
8,766
Reaction score
2,168
Points
113
Location
92346
Alright. After a 45 it looks like more galvanized that's then leaded into a cast iron hub. Thoughts?
so you might have a tiny amount of movement and when you are a foot or so away from pivot point looks worse as the end moves an inch or so. 3 ways to go here cut the arm look inside and if it looks clean just go from there , but again test it with running water . use a Fernco.
2nd way get a good back up on the 45 and try unscrewing but we know it might collapse again.
3rd way go back and remove the lead and oakum (probably pretty easy) I'd try testing and see if its solid by running water no sense taking out the lead if its still not sound connection but my gut says you'll be good at the leaded joint and use a rubber donut
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
That is your lead packed joint there. It's where they shoved the 1.5" galvanized into the 2" hub.
You can either use a 2x1.5 donut or a 2" donut depending on what size pipe you want to use.

index.php


2" donut and 2" pipe
 

Jeff H Young

In the Trades
Messages
8,766
Reaction score
2,168
Points
113
Location
92346
Looks like Mr Love was right about being leaded in!
I think I'd consider a 2 inch trap and arm I'd want to run a snake down at least before calling it good
 

Mr tee

In the Trades
Messages
354
Reaction score
145
Points
43
Location
Montana
I'd get rid of all the galvanized and handle it the way Terry suggested.
 

Modulerics

Member
Messages
31
Reaction score
1
Points
8
Location
New Jersey
That is your lead packed joint there. It's where they shoved the 1.5" galvanized into the 2" hub.
You can either use a 2x1.5 donut or a 2" donut depending on what size pipe you want to use.

index.php


2" donut and 2" pipe
Yep. Had to do it with the toilet flange. I think I'll do that here. I don't want to return old galvanized that already clogged up. Will like do the 2" w the 2 x 1.5 flush bushing inside it then build from there. I like that.

I will say that galvanized is in at a crazy angle which adds to me not liking it and and wanting to remove it.

20221024_152255_copy_1612x1209.jpg
20221024_152300_copy_1612x1209.jpg
 