Conduit for 60V DC

Users who are viewing this thread

JasonG2020

New Member
Messages
21
Reaction score
2
Points
3
Location
Houston
Hello all, I have to run 4/0 wire through a brick wall from my battery bank to an outdoor inverter. The wire will carry a max of 60V. Can I use Schedule 80 PVC conduit, or is EMT or some other type required? The inverter doesn't have much ingress space for a single two-inch conduit. Can I use two one-inch conduit lines from a junction box on the outside of the brick to run each wire to the inverter, or is a single run required? Photos for context.
 

Attachments

  • Exterior Wall_s.png
    Exterior Wall_s.png
    590 KB · Views: 19
  • Sol-Ark Bottom_s.png
    Sol-Ark Bottom_s.png
    549.3 KB · Views: 23
  • Sol-Ark Interior_s.jpg
    Sol-Ark Interior_s.jpg
    50 KB · Views: 21
Last edited:

wwhitney

In the Trades
Messages
6,971
Reaction score
1,973
Points
113
Location
Berkeley, CA
Can I use Schedule 80 PVC conduit, or is EMT or some other type required?
PVC is OK.

The inverter doesn't have much ingress space for a single two-inch conduit. Can I use two one-inch conduit lines from a junction box on the outside of the brick to run each wire to the inverter, or is a single run required? Photos for context.
NEC 300.3(B) would require both conductors to be in the same conduit unless you take some unusual measures, see NEC 300.3(B)(3).

Cheers, Wayne
 