EGAD! The MINIMUM-fire input on the Dunkirk 95M-200 is 80MBH (80,000 BTU/hr) which is enough burner to keep my house toasty even at -100F, if I had enough radiation to emit that much! At the 200 MBH high-fire it's enough boiler to keep my house warm at an outdoor getting closer to absolute zero than my actual outside design temp.
HOW big is this place? (If it's under 10,000 square feet, it's too much boiler.)
The problem with an 80 MBH min-fire output is that there's no way to run a low-mass radiation zone without short-cycling it into lower efficiency and higher maintenance. Even at 190F output (does it go that high?) for a 180F AWT it would take 300' of fin tube to balance boiler out with radiation output. With slab radiant you have some thermal mass to work with (the thermal mass of the concrete), but it's probably short cycling a bit even on those zone calls.
There is clearly no way to install enough radiation on this zone to keep it from cycling. The best thing to do is to size the radiation to be able to deliver the heat at 125F it will fit, and let it short-cycle. The thermal mass of cast iron would help a bit, but not enough. When its time to replace this boiler (and it probably won't make it 20 years, maybe not even 15) be ready to install something more appropriately sized for both the load and the zone radiation. About 19 out of 20 houses could be heated adequately with a condensing boiler with less than 50,000 BTU/hr of maximum output, and 99 out of 100 with something with 75K max, which is your MINIMUM output.
HOW big is this place? (If it's under 10,000 square feet, it's too much boiler.)
The problem with an 80 MBH min-fire output is that there's no way to run a low-mass radiation zone without short-cycling it into lower efficiency and higher maintenance. Even at 190F output (does it go that high?) for a 180F AWT it would take 300' of fin tube to balance boiler out with radiation output. With slab radiant you have some thermal mass to work with (the thermal mass of the concrete), but it's probably short cycling a bit even on those zone calls.
There is clearly no way to install enough radiation on this zone to keep it from cycling. The best thing to do is to size the radiation to be able to deliver the heat at 125F it will fit, and let it short-cycle. The thermal mass of cast iron would help a bit, but not enough. When its time to replace this boiler (and it probably won't make it 20 years, maybe not even 15) be ready to install something more appropriately sized for both the load and the zone radiation. About 19 out of 20 houses could be heated adequately with a condensing boiler with less than 50,000 BTU/hr of maximum output, and 99 out of 100 with something with 75K max, which is your MINIMUM output.