Combi Size accurate?

DIY Pro

New Member
Messages
1
Reaction score
0
Points
1
Location
NJ
Long time reader, first time poster.

Been reading thru the forum while trying to successfully size a new combi to replace my failing 120k btu 1970's gas boiler.

So I'm ordering a new Rinnai combi 090199 unit (90kCH 199kDHW), (min output is 15k) for my older home in NJ that has a manual J calc of approx 50K heat load (loadcalc.net) and 95' of baseboard fin on a single zone over 2 floors. Home is currently being expanded from its existing 2000sqft to 3000sqft.

Does the 90k Combi size seem too large, as I was considering going with the 60kCH 199DHWk Model instead , but was concerned it might be too small after the addition and another 30-40' of baseboard was added

Interested to get some thoughts from the forum regarding my choice of combi size.
 
Back
Top