Code requirements re: GFCI outlet close to toilet

Users who are viewing this thread

Waylo

New Member
Messages
2
Reaction score
1
Points
3
Location
PNW
Hi everyone,

I'm building a home and will be installing an electrical outlet on the back wall adjacent to the toilet to power a bidet. Are there any codes/regulations regarding how close to the toilet an outlet may be?

cst446-03.jpg
 
Last edited by a moderator:

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
I don't believe the NEC specifies a minimum distance between the receptacle and the toilet, just that the receptacle has to be GFCI protected.

It does require that the GFCI device protecting the receptacle be "readily accessible". That means (2014 version): "Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to actions such as to use tools, to climb over or remove obstacles, or to resort to portable ladders, and so forth."

Cheers, Wayne
 

Waylo

New Member
Messages
2
Reaction score
1
Points
3
Location
PNW
Thanks both of you for the quick replies! I went to inspect the site today (electrical just got started this week) and the electrician put them pretty far up on the perpendicular wall instead of on the back wall. Just wanted to check before I tell them to move it.
 