Code Question

Users who are viewing this thread

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
Kind of a trick question.

The laundry room needs one. The dryer can also be plugged into it.

Can another outlet in the same room be on it????
 

jaxbldginspector

New Member
Messages
21
Reaction score
0
Points
0
I think I found the answer:

NEC 220-4 (c) Laundry Branch Circuits-Dwelling Unit. In addition to the number of branch circuits determined in accordance with (a) and (b) above, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by Section 210-52(f). This circuit shall have no other outlets.

Thanks
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
I think I found the answer:

NEC 220-4 (c) Laundry Branch Circuits-Dwelling Unit. In addition to the number of branch circuits determined in accordance with (a) and (b) above, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by Section 210-52(f). This circuit shall have no other outlets.

Thanks


Are you still on the 1996 code cycle?
What you have quoted is from that cycle!
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
washer

And, as an aside, here, when there is an electric dryer, the washer outlet is a single device receptacle so nothing except the washer can be plugged into it.
 

Jbfan74

Electrical Contractor
Messages
135
Reaction score
1
Points
18
Location
Newnan, GA
And, as an aside, here, when there is an electric dryer, the washer outlet is a single device receptacle so nothing except the washer can be plugged into it.

Do you have anything in writing to back up that statement?
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
And, as an aside, here, when there is an electric dryer, the washer outlet is a single device receptacle so nothing except the washer can be plugged into it.
I agree. If that is an actual code there must be a written amendment to back it up.
That certainly is not an NEC requirement.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
outlet

It is just the way the electicians do it, and they do the same with other outlets such as a freezer or garage wall air conditioner that should not be connected to a GFCI so that no one can plug an extension cord into the same outlet and not be GFCI protected while using it.
 

Johnny C

Electrician
Messages
23
Reaction score
0
Points
0
Location
Mass. & now Virginia Beach, VA
Circuit for washing machine

According to the NEC, it allows more than one receptacle outlet to be installed on the 20-ampere laundry branch-circuit. If you have a gas dryer, both the gas dryer and washing machine can be plugged into the same 20-ampere circuit, however, if the UL Labeling and Listing of the products specify that they must be on their own 20-ampere branch circuit, then 110-3(B) takes precedent.
 