Here's a picture of my water heater configuration. The problem I'm having is in the basement and downstairs faucets and things the cold water pipes are running with hot water. I think it's because the hot water is backflowing into the cold wire line supply line and then up into those

IMG_20191104_163411.jpg
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
Can you put your hand on the cold at the wall and see if that's warm?
Normally a check valve prevents the recirc from pushing water that direction. There could also be a crossover somewhere. Sometimes at a shower.
 

Roadman33

I know enough to get in trouble
Messages
37
Reaction score
0
Points
6
Location
Seattle
Can you put your hand on the cold at the wall and see if that's warm?
Normally a check valve prevents the recirc from pushing water that direction. There could also be a crossover somewhere. Sometimes at a shower.
Yeah both pipes coming out of the wall there are piping hot
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,435
Points
113
Location
IL
Go feel the cold lines at different sinks and shower. If you find a hot cold, I think you found your crossover.
 

Roadman33

I know enough to get in trouble
Messages
37
Reaction score
0
Points
6
Location
Seattle
What is the expansion tank is broken? Could that be the problem?
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,435
Points
113
Location
IL
What is the expansion tank is broken? Could that be the problem?
I don't totally understand the question, but the expansion tank would not cause your hot cold water symptom.

The tank should be normally empty if you are running a little water. If the tank fails, or if the precharge air is set too low, the tank would not sound empty when you knock on it.
 

WorthFlorida

Clinical Trail on a Cancer Drug Started 1/31/24. ☹
Messages
5,763
Solutions
1
Reaction score
998
Points
113
Location
Orlando, Florida
If you have one of those auto on faucets it can cause the problem. The faucet hot and cold valves are opened all the time and the auto on/off feature is a valve on the hose to the outlet of the faucet. There should be a built in check valve in the fixture but I'm not sure. If it can't be fixed install a check valve on the cold side that feeds the faucet.
 

Roadman33

I know enough to get in trouble
Messages
37
Reaction score
0
Points
6
Location
Seattle
My expansion tank is bad. It seems full of water. It also is hot on top and cold on the bottom. When I tap on it it just seems dents like it's got no air in it. Anything I should know about replacing it?

If an expansion tank does fail does it make it more likely that the check valve will stay open and that would let hot water backfill in to the system?
 