I’m having a debate with some friends about the best place to put a check valve in conjunction with a RPBA. I always thought it best to put it downstream of the device to prevent nuisance discharge, a colleague said it’s better to put the check valve upstream to absorb any pressure fluctuations coming from the incoming water supply. What say you all?
 

James Henry

In the Trades
Messages
1,574
Reaction score
400
Points
83
Location
Billings, Montana.
Check valves are not installed near a RPBA, The RPBA is a form of check valve, you may already have a check valve at your meter. If your RPBA is constantly discharging or dripping then it needs maintenance.
 

James Henry

In the Trades
Messages
1,574
Reaction score
400
Points
83
Location
Billings, Montana.
I have always assumed that the reduced pressure back flow was all you needed too.

I would think that if you put a check valve down stream of an RPZ you won't know if the RPZ has failed until the check valve fails and then its to late. I 've never heard of putting in a check valve specifically for an RPZ. They are a form of check valve.
 
Last edited:

Jeff H Young

In the Trades
Messages
8,759
Reaction score
2,166
Points
113
Location
92346
My guess is is not prohibited . but I wouldn't recommend it. I'd build it though if on my detail
 