Change from S trap to P trap

Users who are viewing this thread

John Prekup

New Member
Messages
8
Reaction score
0
Points
1
Location
Spring City PA
IMG_7850.JPG
IMG_7849.JPG


Hi everyone,

I have a question in regards to a double vanity in my upstairs 2nd floor bathroom. The house is about 30 years old and I'm currently updating the batroom. It's has a tub shower, toilet, and a double bowl vanity. It currently has S-traps for both of the sinks.

Since I have the bathroom stripped down to the studs and have access to below the floor I was wondering if there would be way to install p-traps and correctly vent these fixtures.
Their are a few problems though....
The wall that is behind where the vanity sits is a 2x4 wall and has a header directly below it. I could pack the wall out 2" and change my toilet from a 12" to a 10" which would gain some space but I can't go any further than that since my toilet flange is right up against the floor joist( that 3"sanitary tee is missing in the picture - It was broken and needs to be replaced).

Top pic shows 2" drain from tub on left into a 3" sanitary tee then 90 to basement

Bottom pic shows two 1 1/2" drains from sink to below floor. Left one goes through floor then 90s into 3" sanitary tee. Right one goes the through floor then to right and loops back to 3" vent.
Vent is 3" that goes to attic through roof.

Any help/ideas on what could be done to make this work would be greatly appreciated.

Thanks,
John
 

Attachments

  • IMG_7844.JPG
    IMG_7844.JPG
    51.1 KB · Views: 238

John Prekup

New Member
Messages
8
Reaction score
0
Points
1
Location
Spring City PA
Some pics from below
 

Attachments

  • IMG_7847.JPG
    IMG_7847.JPG
    66.9 KB · Views: 212
  • IMG_7845.JPG
    IMG_7845.JPG
    55.4 KB · Views: 206
  • IMG_7839.JPG
    IMG_7839.JPG
    76.7 KB · Views: 215

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
double_lav_rough_2.jpg


If your cabinet has a kick space under it, you can use that space like this. Where is the vent that you have now?
Also, those santees on the horizontal should have been wye or combo fittings.
 

John Prekup

New Member
Messages
8
Reaction score
0
Points
1
Location
Spring City PA
Thanks for the reply Terry.

I have not ordered the double vanity as of yet so I could defiantly get one that has the space under it so that would work.

The vent is a 3" that is in the adjacent wall in the 2nd picture. (To the right)

So if I just 90 that 3" vent under the floor and pickup the 2" sink drain with a single 3"x3"x2" wye that would work?
As far as the vent. Could I run that exactly like your pic and 90 around to the 3" stack vent? Shown in my 2nd pic above?

John
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
A 3x2 wye to pick up the lavs, and then in the attic if that's easier for the vent to the 3" vent to the right. Or drill it over at 42" above the floor.
 

John Prekup

New Member
Messages
8
Reaction score
0
Points
1
Location
Spring City PA
Ok that sounds good. Heres what it would kind of look like then.

Tub is not under as this drawing shows but parallel to the 3" (like if you were looking down from the top.

John
image.jpg
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
The tub should come in upsteam of the toilet, not downstream as the drawing shows.
The toilet drops into a wye or combo, not a santee. The tub comes into a wye or combo.
Long or medium sweep on the tub.
You getting closer. :)
 

John Prekup

New Member
Messages
8
Reaction score
0
Points
1
Location
Spring City PA
Terry,

Would this work under floor?

Top of pic would dump to 90 to basement
Toilet off 1st 3" wye
3 x 2" Combo to tub
Right side 2nd 3" wye with 2" reducer to sinks
Left of bottom wye continues to 3" vent through attic roof.
 

Attachments

  • IMG_7857.JPG
    IMG_7857.JPG
    79.7 KB · Views: 200

John Prekup

New Member
Messages
8
Reaction score
0
Points
1
Location
Spring City PA
Ok here is the final rough in. Nothing is glued as of yet in case I need to make changes.

1 1/2 out of top of double sanatee ties into 3" vent in attic

Any concerns?

John

IMG_7859.JPG
IMG_7860.JPG
IMG_7861.JPG
IMG_7863.JPG
 

Asktom

Member
Messages
745
Reaction score
32
Points
18
Location
Victor, MT
You have used a double sanitary tee to split off to the two lavs, it should be a double fixture tee.
 