The ES2-4 doesn't sound right on a number of counts...
The
ES2 series has
not been discontinued, but there may have been recent changes/updates.
However the 89,000 BTU/hr DOE output of the ES2-4 is ridiculously oversized for most normal sized houses (even if you're also using it to heat domestic hot water), and not the best choice for 19 out of 20 houses in your ZIP code. Even the ES2-3 is more than 1.5x oversized for most homes in NYC (ASHRAE recommends 1.4x oversizing, not more.)
It needs a correctly sized flue liner to be vented into a masonry chimney, but it doesn't need to be stainless.
The ES2 is more expensive than several fire-tube modulating condensing boilers out there that would be a better size fit, even at a comparable higher BTU output, and cheaper to install too.
Take a BIG step back, gather up some wintertime-only oil fill up slips, and first
run a fuel-use based load calculation using the oil burner as the measuring instrument to get a handle on your heat load at +15F outdoors (NYC's 99th percentile temperature bin aka "
99% outside design temperature".) The largest cast iron boiler should have a DOE output no more than 1.4x the fuel-use calculated number, but not less than that number.
With a modulating boiler there is more flexibility, but the minimum modulated output becomes the more important number. To get a handle on
that measure up your radiation (zone by zone if multi-zoned.) With the heat load numbers and radiation numbers it's possible to ballpark how much of the time a condensing boiler would actually be delivering condensing efficiency, and how low the water temperature would be before the boiler could potentially short-cycle.
The napkin math on that lives here.
If you can share the fuel use information I can run the load numbers here, if that's any easier.