Burial of copper water lines

Discussion in 'Canadian Plumbing Code Questions' started by Kiton, Aug 29, 2020.

  1. Kiton

    Kiton Member

    Joined:
    Feb 16, 2014
    Location:
    Quebec
    I have searched through the NPC for the rules of burying copper drinking water supply lines.

    The only reference I have found is in the screen capture attached referencing mechanical damage.

    Wayne had sent me the IPC rules for burial but I cant find anything even close in the NPC:

    305.1 Protection Against Contact

    Metallic piping, except for cast iron, ductile iron and galvanized steel, shall not be placed in direct contact with steel framing members, concrete or cinder walls and floors or other masonry. Metallic piping shall not be placed in direct contact with corrosive soil. Where sheathing is used to prevent direct contact, the sheathing shall have a thickness of not less than 0.008 inch (8 mil) (0.203 mm) and the sheathing shall be made of plastic. Where sheathing protects piping that penetrates concrete or masonry walls or floors, the sheathing shall be installed in a manner that allows movement of the piping within the sheathing."

    The reference is to this installation job.

    thanks!!
     

    Attached Files:

  2. Reach4

    Reach4 Well-Known Member

    Joined:
    Sep 25, 2013
    Location:
    IL
    Last edited: Aug 29, 2020
    Kiton likes this.
  3. Sponsor

    Sponsor Paid Advertisement

     
    Kiton likes this.
  4. Kiton

    Kiton Member

    Joined:
    Feb 16, 2014
    Location:
    Quebec
    Thanks Reach4, it is a help actually because part of the issue is he did not seal the hole in the wall from the outside so water can seep inside.
     
  5. Kiton

    Kiton Member

    Joined:
    Feb 16, 2014
    Location:
    Quebec
    Can any Canadian plumbers point me to code on copper pipe being in contact with concrete walls?


    thanks,
     
  6. Kiton

    Kiton Member

    Joined:
    Feb 16, 2014
    Location:
    Quebec
    2.3.5.5. Protection from Mechanical Damage
    1) Plumbing, piping and equipment exposed to mechanical damage shall be
    protected.

    Am I am safe to assume this means copper pipe penetrating a concrete wall must be insulated from contact?

    thank you,
     
  7. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    Anytime I have copper going through concrete it gets wrapped with UPC pipe wrap tape to prevent direct contact.
     
  8. Kiton

    Kiton Member

    Joined:
    Feb 16, 2014
    Location:
    Quebec
    Thank you Terry.
     