BTU Measurement Tool

Users who are viewing this thread

Michael Melvin

New Member
Messages
7
Reaction score
0
Points
1
Location
Massachusetts
Is there such a hand tool that can be attached to the end of a gas line run that can measure the amount of BTU at the END of the run?

We had an outdoor gas firepit installed last fall and the burner is rated for 150,000 BTU. The plumber we hired obviously didnt calculate correctly for this. He ran a 1/2OD poly coated copper pipe from the meter to the fire pit. The run is about 60'-68 feet from the meter.

We are going to replace about 48' with 1" pipe and leave the last 12' as the 1/2"OD (which is under a newly finished brick patio and fieldstone fire pit that ISN'T GETTING TORN UP). I have been told that we can probably get the total BTU up to around 110,000-130,000 depending on which plumber I have asked.

Once this is done I will need to replace the firepit burner with a smaller one based on the BTU so I will need to have a pretty accurate BTU number. This is why I am looking for the total BTU.

Before you chime in...Yes I did paid the first plumber, yes he is licensed, no im not using him again. At this point I need to work with what I have and make it the best I can considering the circumstances. He made a mistake and at the end of the day its not the end of the world. Just trying to make it the best I can at this point. Thank you for your time!
 

Reach4

Well-Known Member
Messages
38,798
Reaction score
4,412
Points
113
Location
IL
I am not a plumber or other pro. If you study your gas meter, can you measure resulting flows in several minutes of flow? If so, you could try an empirical test.

I am thinking put a ball valve and a galvanized pipe at the pit temporarily. Open the valve with flows letting the gas hit the flame of a propane torch to ignite the gas.

I am thinking that whatever the flow is, get a burner of maybe 1/2 that many btu/hour. 1 cuft of gas is about 100,000 BTU of gas, which is 1 therm. So do some math.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
There are calculators you can find online that will let you know how many BTU a particular line can provide based on the ID, the length, and the number of fittings. Here is one, there are lots of others, if you find this one confusing... https://www.engineeringtoolbox.com/natural-gas-pipe-sizing-d_826.html

One possibility might be if you could raise the pressure. That would require, potentially, new pressure regulators on the other devices, but raising the typical pressure from 0.5psi to say 2psi would probably allow you to use the existing line with the full capacity of the grill.
 