Bunny Laroche
New Member
Hello,
I feel somewhat terrible as I only post here when we experience boiler troubles.
Well, when I woke up this morning the temperature in the house dropped to ~60 degrees. The rads were cold to the touch and although the boiler was powered on and appeared normal without any signs of problem, it was not firing when there was a definite call and need for heat.
My GF started to do system checks and observed the following with our Westinghouse 80K BTU boiler:
- the boiler's main display screen displayed no obvious signs of trouble. There were no err codes displayed, and everything appeared normal except the FAN and GAS icons were not present, which makes sense because the boiler was not firing
- the outdoor temperature reported by boiler was correctly reported at ~3 degrees
- voltage reading of the ODS leads: ~4.75VDC, which my GF said should be about right for the temperature sensed outside
- in the boiler's "installer mode" menu, the 1:EH (error history) value was: E0.11, and the manual shows that the default is E0.00. But, when we selected the 1:EH option (pressing the large round dial knob with the Enter symbol) no additional error information was conveyed. We weren't absolutely sure, however, that there might be something more we need to do to access further error history information from this option's menu.
- the TACO valve controller appeared to be operating normally as did the supply and return pumps. The valves were open and the pumps were working because the two zone thermostats were calling for heat.
So, since nothing appeared obviously wrong, my GF powered the boiler off, using the boiler's power switch located on the control board behind the (removed) cover. She left the power off for ~10-15 seconds before turning it back on. The boiler appeared to perform a normal start up procedure, afterwhich we turned the two zone's thermostats back on, one at a time. With a call for heat activating the TACO controller once more, the zone valve opened and two pumps began circulating as expected, and ~5-10 seconds later the boiler fan came on and proceeded to fire up. That was two hours ago and the boiler continues to operate normally with the room temperature rising slowly but steadily.
Our primary concern then, is what might have caused the boiler to stop operating (firing) during the wee hours of the morning when there was a definite call and need for heat? And can we expect it to occur again/often?
My GF also captured these results from a combustion analyser probe inserted into the flue after a 1-2 minute stabilization period. Although the results do not suggest anything wrong, I thought it best to include them for thoroughness.
Testo 310's bottom menu readings:
CO: 15ppm
Eff. : 98.1%
T: 14°C
EXA: 30.9%
CO2: 8.68%
Testo 310's top menu readings:
O2: 5.4%
T: 31.2°C
CO: 3ppm
uCO: 20ppm
I feel somewhat terrible as I only post here when we experience boiler troubles.
Well, when I woke up this morning the temperature in the house dropped to ~60 degrees. The rads were cold to the touch and although the boiler was powered on and appeared normal without any signs of problem, it was not firing when there was a definite call and need for heat.
My GF started to do system checks and observed the following with our Westinghouse 80K BTU boiler:
- the boiler's main display screen displayed no obvious signs of trouble. There were no err codes displayed, and everything appeared normal except the FAN and GAS icons were not present, which makes sense because the boiler was not firing
- the outdoor temperature reported by boiler was correctly reported at ~3 degrees
- voltage reading of the ODS leads: ~4.75VDC, which my GF said should be about right for the temperature sensed outside
- in the boiler's "installer mode" menu, the 1:EH (error history) value was: E0.11, and the manual shows that the default is E0.00. But, when we selected the 1:EH option (pressing the large round dial knob with the Enter symbol) no additional error information was conveyed. We weren't absolutely sure, however, that there might be something more we need to do to access further error history information from this option's menu.
- the TACO valve controller appeared to be operating normally as did the supply and return pumps. The valves were open and the pumps were working because the two zone thermostats were calling for heat.
So, since nothing appeared obviously wrong, my GF powered the boiler off, using the boiler's power switch located on the control board behind the (removed) cover. She left the power off for ~10-15 seconds before turning it back on. The boiler appeared to perform a normal start up procedure, afterwhich we turned the two zone's thermostats back on, one at a time. With a call for heat activating the TACO controller once more, the zone valve opened and two pumps began circulating as expected, and ~5-10 seconds later the boiler fan came on and proceeded to fire up. That was two hours ago and the boiler continues to operate normally with the room temperature rising slowly but steadily.
Our primary concern then, is what might have caused the boiler to stop operating (firing) during the wee hours of the morning when there was a definite call and need for heat? And can we expect it to occur again/often?
My GF also captured these results from a combustion analyser probe inserted into the flue after a 1-2 minute stabilization period. Although the results do not suggest anything wrong, I thought it best to include them for thoroughness.
Testo 310's bottom menu readings:
CO: 15ppm
Eff. : 98.1%
T: 14°C
EXA: 30.9%
CO2: 8.68%
Testo 310's top menu readings:
O2: 5.4%
T: 31.2°C
CO: 3ppm
uCO: 20ppm