I found what I was referring to. Below the pump tables it reads; If you are not using one of the pumps listed in the above tables, use a pump with an integral check valve or install a check valve at the pump outlet.
In this case, I am using a pump from the table
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
I found what I was referring to. Below the pump tables it reads; If you are not using one of the pumps listed in the above tables, use a pump with an integral check valve or install a check valve at the pump outlet.
In this case, I am using a pump from the table

Which pump(s) are you using?
 

Sponger76

New Member
Messages
23
Reaction score
1
Points
3
Location
Ny
I am using the wilo star s 21 f. They do not come with a check valve though so the literature is a little confusing in this instance.
 

Sponger76

New Member
Messages
23
Reaction score
1
Points
3
Location
Ny
This is the reading I am referring to
 

Attachments

  • boiler page.png
    boiler page.png
    119.3 KB · Views: 167

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
I am using the wilo star s 21 f. They do not come with a check valve though so the literature is a little confusing in this instance.

If the Star S-21 is the primary pump (the one driving boiler loop) there is no need for a check valve- it's a pretty beefy pump. In a primary/secondary configuration that primary pump will always be running when any (or all) of the zone pumps are running. If using multiple secondary (zone radiation loop) pumps, the zone pumps each need a check valve to block back flow when the pump isn't operating.
 

Sponger76

New Member
Messages
23
Reaction score
1
Points
3
Location
Ny
Ok thank you again Dana. That wasn't clear on the documentation. I spoke with a local supplier this morning and they said that the inline flange check valves wont work for what I need and that I need stand alone inline check valves. Any suggestions? Name brand, specs etc?
 

Sponger76

New Member
Messages
23
Reaction score
1
Points
3
Location
Ny
I'm fine tuning all the settings on my navien nhb. I have since last time I posted, installed spring check valves and plumbed the p/s manifold in. I am on day 83 of working 12 hour days consecutively and I am tired by the time I get home. My most current question is this. I installed the navien 2 zone ch controller and both the boiler and the controller have dip switches. Both have a thermostat used and unused dip switch. Should both the controller and the boiler be switched to "used" or is this a situation where the boiler thermostat is "unused" because the controller is "used"?
 

Sponger76

New Member
Messages
23
Reaction score
1
Points
3
Location
Ny
Never mind guys. I sat down and read the FMZ 20 manual and now I understand that the boiler "used" dip is if you are using the fmz to run your boiler pump. For example if you didn't have an Navien boiler and you were piecing 2 different brands together, you might not need a boiler pump like I do. So you would enable this dip in this scenario. My navien controls my boiler pump so in my case, the dip is disabled. Thanks again guys. You have been great help. I know someone said I should do the napkin math test (maybe dana?) And I will. BTU's in vs BTU's out. Tomorrow is another day.
 