I have ran several models on the HeatLoad for the Central Heating (CH):
Heat Load Pro is 48K /32K (The 32K is without air leakage)
Dana's method using Energy Bill shows a max of 27K with a min of 3K for the 0 HDD
Weil McLain replacement kit is 56K.
Original Manual-J from 1986 is 78K
Whole Host Load Calculator (quick) is 40K
DHW estimate is for indirect between 55 GA and 72 - which is requires 100 BTUh when all of the bathroom showers are running (which is once a year).
Right now, I am compiling a list of Boilers that can modulate to the lower end, since that covers the majority of the colling.
Navien NHB with 95% AFUE has a range of 8K - 80K
HTP UFT with 95.4 AFUE ranges from 8K to 80K
HTP Versa-Hydro with 93.0% AFUE ranges from 10K to 100K
In reading the manual for the HTP Versa Hydro it will modulate the burner to the tank at 1:7
The modulate the water for the heater exchange at 1:10
Trying to figure out if the HTP Versa Hydro will just draw from the thermal mass of the Indirect tank to heat the CH fluid before it fires the Gas to heat the in-direct. Don't know if the control system has enough smarts in the summer months to not turn on the gas for the 15-30 minutes it takes to heat the basement.
Looking for some practical real-world experience to enlighten this software engineer.
Heat Load Pro is 48K /32K (The 32K is without air leakage)
Dana's method using Energy Bill shows a max of 27K with a min of 3K for the 0 HDD
Weil McLain replacement kit is 56K.
Original Manual-J from 1986 is 78K
Whole Host Load Calculator (quick) is 40K
DHW estimate is for indirect between 55 GA and 72 - which is requires 100 BTUh when all of the bathroom showers are running (which is once a year).
Right now, I am compiling a list of Boilers that can modulate to the lower end, since that covers the majority of the colling.
Navien NHB with 95% AFUE has a range of 8K - 80K
HTP UFT with 95.4 AFUE ranges from 8K to 80K
HTP Versa-Hydro with 93.0% AFUE ranges from 10K to 100K
In reading the manual for the HTP Versa Hydro it will modulate the burner to the tank at 1:7
The modulate the water for the heater exchange at 1:10
Trying to figure out if the HTP Versa Hydro will just draw from the thermal mass of the Indirect tank to heat the CH fluid before it fires the Gas to heat the in-direct. Don't know if the control system has enough smarts in the summer months to not turn on the gas for the 15-30 minutes it takes to heat the basement.
Looking for some practical real-world experience to enlighten this software engineer.