At an average water temperature of 140F the 14' of baseboard is emitting about 4500 BTU/hr and the boiler is out of the condensing zone, delivering about 7000 BTU/hr, so there is about 2500 BTU/hr (42 BTU minute) of excess heat going into the zones.
If there's 40lbs of water in that loop the temperature would have risen more than 10F during a continuous 15 minute burn, which makes me wonder if there are no check valves allowing the other zones to backflow a bit(?). If the zone were completely isolated it would stabilize at 160F-165F if burning continuously in a non-condensing mode. If it's stablizing at temps less than 140F it means there is probably other water being circulated in that loop coming from other radiation.
By running it at 140F+ it's not short cycling- it won't wear out the boiler, but you are giving up all of the condensing efficiency.
As an experiment try setting the post-purge to 5 minutes and watch how quickly the temperature drops when starting at ~140F.
If there's 40lbs of water in that loop the temperature would have risen more than 10F during a continuous 15 minute burn, which makes me wonder if there are no check valves allowing the other zones to backflow a bit(?). If the zone were completely isolated it would stabilize at 160F-165F if burning continuously in a non-condensing mode. If it's stablizing at temps less than 140F it means there is probably other water being circulated in that loop coming from other radiation.
By running it at 140F+ it's not short cycling- it won't wear out the boiler, but you are giving up all of the condensing efficiency.
As an experiment try setting the post-purge to 5 minutes and watch how quickly the temperature drops when starting at ~140F.