Are my "semi-shared neutrals" a problem?

Users who are viewing this thread

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
I don't know what the guy before me had done, but it was pretty weird.

Don't feel bad. I run across things like that all the time. People can do a lot of damage when they know just enough to make the light come on.
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
Okay try reading this one more time.
Slow down and read it slowly so maybe it sinks in

Okay, I have again read what you wrote to someone else and now I understand ... and I thank you for your patience with me and for tolerating whatever attitude I had late last night. A hundred-dollar rebate I have been waiting for from one of the box stores arrived yesterday, and I will get the right wire (if they have it) tomorrow.

... [your drawing] does not make any sense and I am being helpful by taking the time to provide you with crude but accurate drawings.

I thank you for your effort, and your drawings have pretty much helped to confirm my suspicion about another circuit I will mention in just a minute. But first, maybe this will help as to mine:

I did not know how to draw the 3-way switches, so you see a switch with two wires connected at one end. Then, the little "c" indicates the respective commons for the two circuits involved. A piece of 14-2 w/ground takes power to the far switch, then a piece of 14-3 w-ground runs back to the other ... and that is the piece that needs to be 14-4 or whatever so the lower light can have a neutral connected at the box where the power arrives at the upper switch.

And now ...

My living room appears to have a 3-way circuit for the light/fan fixture on the ceiling, but that circuit has not worked properly as a 3-way since we first got this place over four years ago. Having learned a little about 3-way circuits over these past few days, I today spent quite a bit of time trying to make that circuit work like I had believed it should ... but now I believe that is not going to be possible, and here is why I say that:

After disconnecting all the wires and checking the switches to be sure they are good, I identified the runners going from one switch to the other. They are the two black wires in the picture below, and they show no resistance when they are nutted together on the other end. However, the upper black wire on that switch shows continuity (with some resistance) with the disconnected white wire when the pull switch on the ceiling light is on ... and that means I do not really have two runners, correct?
 

Attachments

  • switch2.JPG
    switch2.JPG
    45.3 KB · Views: 296
Last edited:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Here is a good example of why these type of discussion forums can not be used to give advice to someone looking for advice.

Although the subject matter did not change and others were asking questions not everyone reads all post.

Okay, I have again read what you wrote to someone else and now I understand ...

Although someone asked the question that Lee didn’t ask the answer was directed to the original post as much as to the person who asked the question the post was directed to.

There is no way that lessons in electrical can be given over a discussion forum simply due to the fact that there is no control over the reader of the forum.
Most will read only that parts that they agree with and ignore the ones they disagree with. In a classroom setting this can not happen as the person seeking knowledge will here (read) every question and answer.

Lee
How many conductors are in the box in the picture?
2- blacks and 2- whites?
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
Here is a good example of why these type of discussion forums can not be used to give advice to someone looking for advice ...

No, the problem there was your view of the entire world as a classroom with you at the front ... but I digress ... ;)

Lee
How many conductors are in the box in the picture?
2- blacks and 2- whites?

No, just two blacks and one white. And, the other end of this circuit has the same, plus a power lead ... and that is where I get lost. Based on many other wiring troubles I have already encountered and fixed around here, I suspect somebody before me either knew even less than me or never revealed his ignorance by asking questions.

I tried hooking the white wire in the picture below to the common, then connecting the power and blacks ... but that gave me absolutely nothing at the light on the ceiling.
 

Attachments

  • switch1.JPG
    switch1.JPG
    17.2 KB · Views: 287
Last edited:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
No, the problem there was your view of the entire world as a classroom with you at the front ... but I digress ... ;)



No, just two blacks and one white. And, the other end of this circuit has the same, plus a power lead ... and that is where I get lost. Based on many other wiring troubles I have already encountered and fixed around here, I suspect somebody before me either knew even less than me or never revealed his ignorance by asking questions.

I tried hooking the white wire in the picture below to the common, then connecting the power and blacks ... but that gave me absolutely nothing at the light on the ceiling.


In your little picture you have the following labeled.

One white
Two blacks
Power
Common??

This adds up to five

Two simple questions;

How many cables come into the box and how man conductors in each cable?

In my experience I have always seen two wire cable with one white and one black. In three wire cable it is one black one white and one read.
How has this box ended up with two blacks and only one white?

What are you calling a common? What color is this wire you are calling common?

In a three way switch configuration the common screw of the switch will always get either the switch leg or the supply. One switch will receive the switch leg on the common screw and the other switch will receive the supply on the common screw. There is no common wire.

Now as to this remark:
No, the problem there was your view of the entire world as a classroom with you at the front ... but I digress ... ;)
Let me explain a little something that may improve our relationship.
You have come here seeking help. I am willing to assist you in this adventure of yours without any compensation. This makes you the student, the one seeking knowledge, and me or anyone else that is trying to aid you the instructor, the one standing in front of YOUR classroom not the entire world.
3_3_101.gif


Then there are many that come and read the same thread trying to learn something about the same question you have making them a student of the same classroom. See how these discussion forums work? They aren’t a thing but the experienced trying to give freely of their knowledge to those that have neither knowledge nor experience making these forums nothing more than a quick lesson classroom.

Now do you want to accept the help or not?
 
Last edited by a moderator:

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
In your little picture you have the following labeled.

One white
Two blacks
Power
Common??

This adds up to five

Yes.

Two simple questions;

How many cables come into the box and how man conductors in each cable?

In my experience I have always seen two wire cable with one white and one black. In three wire cable it is one black one white and one read.
How has this box ended up with two blacks and only one white?

Four cables come into the box by the door (second picture):

1) One with two conductors for the porch light (and irrelevant here);
2) One with a line (black) and a common (white) and no ground wire;
3) One with a black (runner?) and a white (for a purpose presently unknown);
4) One with a black (runner?) and a white that had been clipped short.

So, and concerning the circuit in question: The box ended up with two blacks and only one white when somebody long ago apparently ran a second cable to get only a black runner (and clipped its unneeded white).

What are you calling a common? What color is this wire you are calling common?

It is the white wire in #2 above that I am calling a common, and that cable is the one that brings power to the 4" box. The switch you can see in picture #2 is the switch for the porch light, and it is connected to the conductors in cable #2 and works just fine.

In a three way switch configuration the common screw of the switch will always get either the switch leg or the supply. One switch will receive the switch leg on the common screw and the other switch will receive the supply on the common screw. There is no common wire.

Understood ... but the white wire in cable #3 above might be the common side of the light if the white wire in picture #1 is its feed, and if so, it would need to be connected to the common in cable #2 in order to complete the circuit for the light.

I am willing to assist you in this adventure of yours without any compensation ...

Now do you want to accept the help or not?

Of course, and I thank you!

Give me about an hour and I will come back with an accurate sketch of the known absolutes related to this circuit. Logic suggests we might be able to figure out the unknowns after making some readings with the power off ...
 
Last edited:

Cookie

.
Messages
5,580
Reaction score
8
Points
0
Location
Home
I am not putting anyone else down in saying this, Lee has an attitude that everyone could learn from.
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
I am not putting anyone else down in saying this, Lee has an attitude that everyone could learn from.

Well, maybe, but some people see me as a well-seasoned, passive-aggressive manipulator ...

But whatever the case, I greatly respect the vast knowledge and experience available here, and I am genuinely grateful to the many who freely share it.

JW: Here is a sketch, and my son-in-law is going to flip and pull switches while I record some readings. So, back in a while ...
 

Attachments

  • livrm3way.jpg
    livrm3way.jpg
    15.8 KB · Views: 288

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
In your little picture you have the following labeled.

One white
Two blacks
Power
Common??

This adds up to five
Yes.
But here you say:
No, just two blacks and one white.
Which leaves the rest of what is in that box in question. We need to know every conductor that enters that box in order to figure out what the person that made the installation was doing.

Four cables come into the box by the door (second picture):
1) One with two conductors for the porch light (and irrelevant here);
2) One with a line (black) and a common (white) and no ground wire;
3) One with a black (runner?) and a white (for a purpose presently unknown);
4) One with a black (runner?) and a white that had been clipped short.
1- Yes it is very relevant as without know what is in the switch box it would be impossible to give an answer.
2- This is the supply (I think) which would have one black hot and one white grounded neutral but not a common.
3- Not a runner and we will figure out what the white is for as we go along
4- A bad idea although it was common practice just after the knob and tube days when electricians was learning how to use cable. This method has never been a code compliant method of installing three way switches.

So, and concerning the circuit in question: The box ended up with two blacks and only one white when somebody long ago apparently ran a second cable to get only a black runner (and clipped its unneeded white).
I have never in 42 years of doing electrical work ever heard of a runner except for the young man that kept running back and froth from the job and the van or port-a-john.
It is the white wire in #2 above that I am calling a common, and that cable is the one that brings power to the 4" box. The switch you can see in picture #2 is the switch for the porch light, and it is connected to the conductors in cable #2 and works just fine.
It is important that when talking about electrical circuits to use the correct terminology so there won’t be a lot of confusion.
We'll quit calling the grounded neutral conductor a common conductor. In premises wiring the grounded neutral is not a common conductor. On a three way switch there is a common screw and this screw will always get a hot or a switch leg.
If the porch light is using the 2 two wire cables then I would think that the two white conductors are under a wire nut and the two blacks are on the switch. Is this correct?
If this is correct so far then the three wires left;
3) One with a black (runner?) and a white (for a purpose presently unknown);
4) One with a black (runner?) and a white that had been clipped short
are for the three way switch. These wires will in no way connect to the conductors in the 2 two wire cables connected to the porch light.
Understood ... but the white wire in cable #3 above might be the common side of the light if the white wire in picture #1 is its feed, and if so, it would need to be connected to the common in cable #2 in order to complete the circuit for the light.
Again it ain’t called a common wire just because it is white. It would be better to call it a “cracker†wire than a common wire. (a little humor there)
When you started this line of questioning about these three way switches in this post how many conductors and cables are in this switch? Is it is like the first one with a cut white wire in one of the cables? Are there three two wire cables in that switch box?
Give us a little more information here please.

I will venture so far as to say I don't think you are going to get the fan and light to work separately of each other just because there aren't enough switches.
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
We need to know every conductor that enters that box in order to figure out what the person that made the installation was doing.

There are two conductors (a black and a white) coming in to get power for the porch light;
There are two conductors (a black and a white) bringing power in from the panel in the basement;
There are two more blacks coming in from the "out" terminals of the 3-way switch across the room;
There is one more white coming in from somewhere presently unknown.

... the supply (I think) which would have one black hot and one white grounded neutral but not a common.

Yes, and I will try to remember "gounded neutral" rather than "common".

On a three way switch there is a common screw and this screw will always get a hot or a switch leg.

Understood and identified.

If the porch light is using the 2 two wire cables then I would think that the two white conductors are under a wire nut and the two blacks are on the switch. Is this correct?

Yes.

If this is correct so far then the three wires left ...

Yes, but remember we still need to power this 3-way circuit. The power for this 3-way circuit is not supplied at its other end.

3) One with a black (runner?) and a white (for a purpose presently unknown);
4) One with a black (runner?) and a white that had been clipped short are for the three way switch.
These wires will in no way connect to the conductors in the 2 two wire cables connected to the porch light.

Understood.

When you started this line of questioning about these three way switches in this post how many conductors and cables are in this switch? Is it is like the first one with a cut white wire in one of the cables? Are there three two wire cables in that switch box?
Give us a little more information here please.

The white and one of the blacks is a cable, the other black is a single strand and there are no more wires and no power coming into that box.

I will venture so far as to say I don't think you are going to get the fan and light to work separately of each other just because there aren't enough switches.

Beyond that, there is no separate fan wire going to the fixture.
 
Last edited:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
In the box that only has one switch there is a cable with a black and white wire. This will be three wires for the three screws

In the box with two switches there is a supply of one black and one white, a switch leg going to the porch light, a two conductor cable and a two conductor cable with the white cut off.

Aside from the code violations of not having all conductors of the same circuit in the same cable which will result in the heating of the single conductor we don’t have enough conductors to make the three way switches work.

Try this. Use the single black wire in both boxes for the common screw of the three way switches. Use the two wire cable in each box for the other two screws on the three way switches and let me know what happens.

Leave the two, two conductor cables for the porch light as they are.

Edited to add;

If I am slow to answer it is because I am watching the ball game. NC is kicking a.............. somehting
 
Last edited:

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
If I am slow to answer it is because I am watching the ball game. NC is kicking a..............

... uh, apples?!

Anyway, case solved ...

In the box that only has one switch there is a cable with a black and white wire. This will be three wires for the three screws

Connected.

In the box with two switches there is a supply of one black and one white, a switch leg going to the porch light, a two conductor cable and a two conductor cable with the white cut off.

Yes, and the problem here is that whoever did the initial work evidently clipped the wrong white! It is the *other* white in that box we have been talking about that goes nowhere.

My son-in-law and I have pulled the fixture down from the ceiling to trace the wires that are there, and we found two cables nutted together as "hot" and "neutral" for the light/fan. However, the white in the cable going to the box by the front door is the one that is clipped, and we cannot find the far end of the other white in that box we have been talking about.

Aside from the code violations of not having all conductors of the same circuit in the same cable which will result in the heating of the single conductor we don’t have enough conductors to make the three way switches work.

Actually, we do ... but yes, I do understand this circuit needs to be completely rewired. In any case, the single wire in the far box is the black in the cable with the white going nowhere, and connecting the two blacks at the ceiling together would be the second "runner" or whatever for the "outs" on the 3-way switches. Then, the whites at the fixture could be the hot and neutral for the light ... but that would be dependent upon being able to make a solid and safe connection to the clipped wire in the box by the door ... and I do not know any way to do that.

Try this. Use the single black wire in both boxes for the common screw of the three way switches. Use the two wire cable in each box for the other two screws on the three way switches and let me know what happens.

My brain is too tired to contemplate that at the moment, but I will roll it around a little later this evening while my son-in-law and daughter are gone and my three grandchildren are ever-so-quietly just sitting and watching me think, eh?!

Leave the two, two conductor cables for the porch light as they are.

You bet, and I thank you and everyone else.
 