Arcoleader bleeding

Users who are viewing this thread

Willep74

New Member
Messages
3
Reaction score
0
Points
1
Location
Coeur d'Alene, Idaho
Hello!

Awesome site here. I was looking for instructions on how to bleed the air out of one of my circuits as I had tomove a baseboard for a remodeling project. I have checked all over but have not been able to find bleeding instructions that match my set up as I have no shut off at the return side and only one spigot on each circuit. The yellow handle in the picture goes to, what looks like, a purge tank. I can post additional pictures and any help is much appreciated!
Thanks!
 

Attachments

  • 20150930_193057.jpg
    20150930_193057.jpg
    63.1 KB · Views: 560
  • 20150930_193023.jpg
    20150930_193023.jpg
    69.3 KB · Views: 502
  • 20150930_192948.jpg
    20150930_192948.jpg
    80.5 KB · Views: 943

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
That's an expansion tank, not a "purge tank". It needs to be filled with air, not water.

Ideally there would be a bleeder valve on the baseboards/radiators somewhere near the highest elevation on the system, which would allow you to eliminate the major quantity of air on the system, to the point where the circulation pump would be capable pushing water through those loops.

Somewhere on the system there is usually an air-vent & bubble trap/scoop to catch and purge the smaller bubbles as they pass by.

Variations on air vents:

With trap:

boiler-air-separator.jpg


Without trap:

22.jpg


Radiation air bleeder variations:

baseboard-s.jpg


bleed_valve.jpg


Close up of a common type of radiation air-bleeder valve, sold at box stores:

2a46d667-0500-4545-8a5f-cd71f3a09e7a_145.jpg
 

Willep74

New Member
Messages
3
Reaction score
0
Points
1
Location
Coeur d'Alene, Idaho
That's an expansion tank, not a "purge tank". It needs to be filled with air, not water.

Ideally there would be a bleeder valve on the baseboards/radiators somewhere near the highest elevation on the system, which would allow you to eliminate the major quantity of air on the system, to the point where the circulation pump would be capable pushing water through those loops.

Somewhere on the system there is usually an air-vent & bubble trap/scoop to catch and purge the smaller bubbles as they pass by.

Variations on air vents:

With trap:

boiler-air-separator.jpg


Without trap:

22.jpg


Radiation air bleeder variations:

baseboard-s.jpg


bleed_valve.jpg


Close up of a common type of radiation air-bleeder valve, sold at box stores:

2a46d667-0500-4545-8a5f-cd71f3a09e7a_145.jpg
So I found the bleeder valve at the highest point and when I opened it water came out right away. I will try to post some pictures of the valve and the bubble trap.
Thanks again for the help!
 

Attachments

  • 1445914893700-1484447840.jpg
    1445914893700-1484447840.jpg
    67.7 KB · Views: 504
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks