Thanks for everyone's help thus far. I think I am now down to my final question, and hopefully it's not too tough. Let me describe my setup again:
1 x Navien CH240 combi boiler
2 x Trane TAM7 air handler w/ hydro coils (1 zone up, 2 zones down w/ Honeywell HZ211 zone controller)
Problem is that the Navien has fixed DHW priority (no way to change) and BOTH AH's are not cycling down / continue to blow the fan with cold water circ'ing during a long DHW call. The TAM7's have supply aquastats but they don't seem to do too much... per the startup (and my testing) cold water will only delay - but not prevent - startup. Similarly, if they are already running, it will not stop them.
My plan is to pick up a couple of third party strap-on aquastats to sever the heat call during times of cold water. What I am unsure of is where exactly to wire them. Is it as easy as splicing it into W?
If so the only other question is, if I went to a multistage stat/ZC, would severing W1 also disable W2/W3 or would I need to cut them at the proper time as well? It seems that for full fan speed the AH needs all three engergized (hence needing to jumper W1-W3) though I have not tested it extensively.
Finally, assuming this all works, I'm open to any suggestions on which model/brand aquastat to purchase. Thanks again!
1 x Navien CH240 combi boiler
2 x Trane TAM7 air handler w/ hydro coils (1 zone up, 2 zones down w/ Honeywell HZ211 zone controller)
Problem is that the Navien has fixed DHW priority (no way to change) and BOTH AH's are not cycling down / continue to blow the fan with cold water circ'ing during a long DHW call. The TAM7's have supply aquastats but they don't seem to do too much... per the startup (and my testing) cold water will only delay - but not prevent - startup. Similarly, if they are already running, it will not stop them.
My plan is to pick up a couple of third party strap-on aquastats to sever the heat call during times of cold water. What I am unsure of is where exactly to wire them. Is it as easy as splicing it into W?
If so the only other question is, if I went to a multistage stat/ZC, would severing W1 also disable W2/W3 or would I need to cut them at the proper time as well? It seems that for full fan speed the AH needs all three engergized (hence needing to jumper W1-W3) though I have not tested it extensively.
Finally, assuming this all works, I'm open to any suggestions on which model/brand aquastat to purchase. Thanks again!