Another Venting Question

Users who are viewing this thread

Arca

New Member
Messages
21
Reaction score
1
Points
3
Location
Ohio
Hi everyone,

I am running a new 2" vent for a master bath and have run into a little problem.

I am using an old vent's roof location. I raised the ceiling of the master to 8', and have now discovered that I do not have the proper 1' clearance from the roof to my 3x2 reducer. I am at about 7.5" from the "high side" of the vent.

My question is...can I extend that 3" pipe length horizontally? I would come down 7.5" from the roof, glue a 3" 90 and then continue with 3" pipe the needed length to my reducer.

I know this may not work, but with that being said can someone provide me with a little education on this section of plumbing code? I understand it is for frost and condensation?

Thanks everyone!

EDIT: Here is a sketch.
 

Attachments

  • Vent.png
    Vent.png
    110.7 KB · Views: 148
Last edited:

Arca

New Member
Messages
21
Reaction score
1
Points
3
Location
Ohio
Can't you just put the 3x2 reducer in the wall below the roof penetration?

Here's the relevant code section:

https://up.codes/viewer/ohio/ipc-2015/chapter/9/vents#903.2

If your insulation is in the ceiling rather than between the rafters, that section requires the 3x2 reducer to be at least 12" below the bottom of the ceiling joists.

Cheers, Wayne

Thanks Wayne, we are going to spray foam in between the roof rafters, not ceiling joists. Will that make a difference?
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,435
Points
113
Location
IL
I am not saying that a reducer is or is not OK where your sketch shows, but I think it should be a
3" x 2" PVC Schedule 40 Eccentric Reducer
429-338e-3.jpg
A regular reducer would leave a little mosquito-breeding pool I fear.

 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
Thanks Wayne, we are going to spray foam in between the roof rafters, not ceiling joists. Will that make a difference?
I would start measuring the 12" from the warm side of the spray foam. That's the thermal envelope.

What's going on to the right of your sketch? I'd consider making the entire horizontal run 3". I think there's some code language about the vent being arranged to drain, so any reducer on the horizontal would be required to be eccentric.

Cheers, Wayne
 

Jeff H Young

In the Trades
Messages
8,931
Reaction score
2,231
Points
113
Location
92346
I would run 3 inch vent horrizontal then reduce on the vertical. Never seen a eccentric reducer in a dwv system used I dont think it meets code but it might
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,435
Points
113
Location
IL
I would run 3 inch vent horrizontal then reduce on the vertical.
That would look better.

Arca, 45 off of vertical is considered vertical. So you could put a 45 where you have the 3-inch 90 drawn, and go down again with another 45.
 

Arca

New Member
Messages
21
Reaction score
1
Points
3
Location
Ohio
Thanks everyone...great idea on the 45s...that will give me my 12" of vertical below the roof.
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
A couple comments:

- If you are able to use a reducer coupling on the 45 degree section, then you won't create any region that can collect water:

https://www.supplyhouse.com/Spears-P102-338-3-x-2-PVC-DWV-Reducer-Coupling

- The 12" length is supposed to be "inside the thermal envelope," which isn't so precisely defined. If you have, say, 6" of spray foam up against the plywood roof deck, I would conservatively say that the thermal envelope is located 6" below the roof deck, so you'd need 18" of 3" pipe below the roof deck. It would be reasonable to argue that the thermal envelope is the middle of the 6" insulation thickness, so you'd only need 15" of 3" pipe below the roof deck. I would argue against using only 12" of 3" pipe below the roof deck.

Cheers, Wayne
 

Arca

New Member
Messages
21
Reaction score
1
Points
3
Location
Ohio
A couple comments:

- If you are able to use a reducer coupling on the 45 degree section, then you won't create any region that can collect water:

https://www.supplyhouse.com/Spears-P102-338-3-x-2-PVC-DWV-Reducer-Coupling

- The 12" length is supposed to be "inside the thermal envelope," which isn't so precisely defined. If you have, say, 6" of spray foam up against the plywood roof deck, I would conservatively say that the thermal envelope is located 6" below the roof deck, so you'd need 18" of 3" pipe below the roof deck. It would be reasonable to argue that the thermal envelope is the middle of the 6" insulation thickness, so you'd only need 15" of 3" pipe below the roof deck. I would argue against using only 12" of 3" pipe below the roof deck.

Cheers, Wayne

Got it and agree, Wayne. I am probably going to go higher than the minimum 12 inches outside of the roof in order to get a good 3" run below the insulation. Thanks for all your help sir.
 