Amp match generator backup 1 1/2 HP well pump

Users who are viewing this thread

PaulaK

New Member
Messages
11
Reaction score
0
Points
1
Location
Tennessee
Looking to get a generator for backup. I read you have to match the amps as well as the wattage.
Anyone set one up and it worked. Questions on the startup watt needing the generator to be of such like high wattage?
 

ThirdGenPump

In the Trades
Messages
184
Reaction score
29
Points
28
Location
MA
3kw will run it but probably won't start it. Manufacturers suggest matching the peak or surge rating of the generator to 'locked' rotor amps. On a 1.5hp you'd be looking at generators with a surge of 10kw. My experience says you could do it with less but that's what they recommend.
 