Well, you could dry vent the shower and use that to wet vent the WC. The deep sink drain would have to be kept separate from the shower/WC drain until downstream of the WC. The shower trap outlet could point towards the nearby wall at a 45 (assuming there's no convenient wall between the shower and the WC); the shower drain can run under the wall for a bit so a dry vent an be taken off, then it can join the WC drain via a horizontal wye, and then the deep sink drain could join in.
Or you could use the dry-vented lav to wet vent the shower and the WC. To do that, the deep sink would again have to run separately to downstream of the WC, as would the kitchen sink. The lav drain would run maybe up and to the right (on your floor plan picture) to get to the right side of the WC; then it could pick up the shower and the WC, or vice versa (but the WC and shower can't combine before hitting the lav); then the deep sink and kitchen sink can join in.
Or you could try circuit venting, depending on the answer to a question I posed here:
https://terrylove.com/forums/index.php?threads/circuit-venting-question.91391/ You'd make the horizontal drain from the deep sink to the WC 3" all the way (a requirement of circuit venting); and you'd take off a dry vent from the horizontal drain for the circuit vent. That would definitely be OK taken off between the shower and WC (which would require running the horizontal drain under a wall like in the wet vent option), but it would be nice to take off just downstream of the deep sink joining in, so it can rise in the same wall as the deep sink vent (and join it at least 6" above deep sink). I'm just not quite sure if that second location is allowed for circuit venting, though.
Cheers, Wayne