Adding a second vanity sink

Users who are viewing this thread

Reach4

Well-Known Member
Messages
38,880
Reaction score
4,433
Points
113
Location
IL
Minimum distance between what and what? Are you talking 1st floor or second floor?

The horizontal purple lines must be at least 6 inches above the flood level of the lavatories below them.
 

wwhitney

In the Trades
Messages
6,563
Reaction score
1,844
Points
113
Location
Berkeley, CA
Not sure I follow the question, but a horizontal vent, or a joint between two vents, needs to be at least 6" above the flood rims of any fixtures served. Just 6" is enough.

Cheers, Wayne
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks