A/C fan doesn't work in auto position, only on position

Users who are viewing this thread

Spanky

New Member
Messages
3
Reaction score
0
Points
1
Location
Mays LAnding, NJ
I have a Honeywell RTH111 series thermostat. When in a/c mode, the fan won't come on when in AUTO position, only when in ON position. It was installed on the oil furnace this winter. Any help will be greatly appreciated. Thank-you.
 

WorthFlorida

Clinical Trail on a Cancer Drug Started 1/31/24. ☹
Messages
5,763
Solutions
1
Reaction score
998
Points
113
Location
Orlando, Florida
You have a thermostat problem. You may need to recheck your wiring and be sure it is in the cool mode. The difference is in heat mode the fan is usually controlled by the heating unit, in your case oil furnace. It allows the plenum to heat up first before turning on the blower to reduce cold air being moved and condensation in the plenum.

In cool mode the fan is controlled by the thermostat. The Auto Fan mode closes a contact to bring the 24 volts AC from the red wire to the green wire immediately when it calls for cooling. The green wire should be wired to the fan controller in the air handler or the blower/fan in your furnace.

You need at least four wires at the thermostat. Green is generally used for the fan at both ends but it be any color if old thermostat wire did not have a green wire. From your description is seems like it is wired correctly however with a voltage meter you can test the thermostat is functioning correctly. Also check that your furnace controller is optioned for cooling. I'm assuming you have a oil furnace air handler and the a coil for the ac is mounted after the unit in the duct work. Is this a new install or something that just stop working?

https://www.manualslib.com/manual/581810/Honeywell-Rth111.html?page=4#manual
 
Last edited:

Fitter30

Well-Known Member
Messages
4,364
Reaction score
799
Points
113
Location
Peace valley missouri
All cooling stats energize the g terminal when calling for cooling. Did your old stat have Rc &RH wires? This stat isn't set up for a two transformer system.
 

Spanky

New Member
Messages
3
Reaction score
0
Points
1
Location
Mays LAnding, NJ
You have a thermostat problem. You may need to recheck your wiring and be sure it is in the cool mode. The difference is in heat mode the fan is usually controlled by the heating unit, in your case oil furnace. It allows the plenum to heat up first before turning on the blower to reduce cold air being moved and condensation in the plenum.

In cool mode the fan is controlled by the thermostat. The Auto Fan mode closes a contact to bring the 24 volts AC from the red wire to the green wire immediately when it calls for cooling. The green wire should be wired to the fan controller in the air handler or the blower/fan in your furnace.

You need at least four wires at the thermostat. Green is generally used for the fan at both ends but it be any color if old thermostat wire did not have a green wire. From your description is seems like it is wired correctly however with a voltage meter you can test the thermostat is functioning correctly. Also check that your furnace controller is optioned for cooling. I'm assuming you have a oil furnace air handler and the a coil for the ac is mounted after the unit in the duct work. Is this a new install or something that just stop working?

https://www.manualslib.com/manual/581810/Honeywell-Rth111.html?page=4#manual
Thank you for your help. I'll try it and let you know how it goes. Also, thanks for the link to the manual.
 

Fitter30

Well-Known Member
Messages
4,364
Reaction score
799
Points
113
Location
Peace valley missouri
Since the fan runs in the on position and not cool auto sounds like a bad stat if the condensing unit runs. Have you waited the 5 minutes for the condenser to turn on ?
 
Last edited: