How do I get vent 6 inches above the flood rim for a floor si
Screenshot_20220420-195915_Gallery.jpg
 
Last edited:

John Gayewski

In the Trades
Messages
4,324
Reaction score
1,319
Points
113
Location
Iowa
The drain runs under the near wall or very close to it. Then you rise at the trap arm. There you go a clear as mud answer for a clear as mud question.
 

Reach4

Well-Known Member
Messages
38,797
Reaction score
4,412
Points
113
Location
IL
Yes. Dry vent is horizontal, and should not be. Run the trap arm from the shower trap, or whatever the fixture is, to the wall. Join the vent, and turn back toward the bottom of your picture.

Alternatively, if you can run the vented lavatory drainage to join the shower drainage, that can be a horizontal wet vent. Use 2 inch below the lavatory sanitary tee.
 