40/60 pressure swith is turning on at 20 and off at 40. What's going on?

Users who are viewing this thread

Jim Goodman

JEG in Raleigh
Messages
48
Reaction score
5
Points
8
Location
Raleigh, NC
My pressure tank is in a utility room in my house. I have a 44-gallon Well-X-Trol WX-250 pressure tank. The pressure tank was installed in 2012 while I was building the house, but did not come into use until 2016 when we moved in. I have a Cycle Stop Valve on my system immediately before the pressure tank. I have a 40/60 Square-D pressure switch on the system. A new well pump was installed 3 years ago and I installed the CSV, a Cycle Sensor electrical control, and a new pressure switch at that time and our well system has worked perfectly since then. Also, FYI, at the time that I installed the new pressure switch and CSV, I also checked and slightly topped up the air in the pressure tank, because it was slightly low per the specs.

Anyway, today I happened to glance at the gauge on my pressure tank and saw that it was down to close to 20 PSI, but not quite at 20 PSI yet. I was pretty certain that I had installed 40/60 pressure switch and I took the cover off and verified that indeed, it is a 40/60 switch. So, I turned on a faucet and watched the pressure in the tank slowly drop to 20 PSI and the switch kicked on and filled the tank, and shut off at 40 psi.

Can someone explain to me what is going on?

QUESTION 1. If the pressure switch is a 40/60 switch, what would cause it to be acting like a 20/40 switch? It is maintaining a 20 PSI spread between switch-on and switch-off, but if it was factory calibrated at 40/60, I would think if it were broken it would not be working at all. I'm completely baffled.
QUESTION 2. Do I need to re-check the air pressure in the top of the tank, and would that have anything to do with this?

QUESTION 3. Is there something broken that I need to replace?

I just don't understand at all what is going on with this and hope someone can explain. We are not having any problems with our water pressure, but maybe that's because the CSV is kicking in and camouflaging a problem associated with the pressure tank or pressure switch. Thanks for any help.
 

Jim Goodman

JEG in Raleigh
Messages
48
Reaction score
5
Points
8
Location
Raleigh, NC
Maybe it's your gauge? Did you verify it?
I did not verify it, but I also replaced that with a good, liquid-filled gauge when I replaced the pressure switch and the fact that the gauge is reading exactly 20 PSI difference between on and off points leads me to think that it's OK.....but I will keep that thought in the back of my mind as something to check no other ideas pop up. Thanks.
 

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
When the pump is not running, the water pressure gauge and air pressure on the pressure tank should be close. Just a simple $0 confirmation test.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
A quick sanity check is to measure the air pressure when the pump has reached cutoff. It should read the same as the water pressure.
 

Jim Goodman

JEG in Raleigh
Messages
48
Reaction score
5
Points
8
Location
Raleigh, NC
When the pump is not running, the water pressure gauge and air pressure on the pressure tank should be close. Just a simple $0 confirmation test.
.........and if after checking, the pressures are significantly different, what might that mean? If the tank pressure is higher than the gauge, what could that mean? And if the tank pressure is lower than the gauge, what might that mean? Thanks.
 