4" Horizontal Cleanout Question ???

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by RiverLodge, Nov 1, 2018.

  1. RiverLodge

    RiverLodge Member

    Joined:
    Oct 27, 2018
    Location:
    Paradise Valley, MT.
    Anyone foresee any potential problems with attached images 6.jpg and 7.jpg with regards to the 4"clean out and 2" convenience drain?

    Or would a 4X4X2 90 Degree Low Heel Inlet Elbow at the bottom of vertical stack be a better option?

    Thanks in advance for your response.
    RL
     

    Attached Files:

    • 6.jpg
      6.jpg
      File size:
      55.3 KB
      Views:
      95
    • 7.jpg
      7.jpg
      File size:
      49.8 KB
      Views:
      224
    • Low Heel.jpg
      Low Heel.jpg
      File size:
      9.3 KB
      Views:
      89
  2. Reach4

    Reach4 Well-Known Member

    Joined:
    Sep 25, 2013
    Location:
    IL
    I think everybody will prefer your photos of the wye and 45 to the low heel elbow.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. RiverLodge

    RiverLodge Member

    Joined:
    Oct 27, 2018
    Location:
    Paradise Valley, MT.
    So this is acceptable? Seems like debris could accumulate over time in the horizontal section of the clean out wye.
     
  5. Sylvan

    Sylvan Still learning

    Joined:
    Sep 23, 2004
    Occupation:
    plumbing - fire suppression - boiler inspector
    Location:
    New York
    If the lines are properly pitched there will still be some debris by the CO plug but a CO should be full size up to 4" and piping over 4" should have a co no less than 4"
     
Similar Threads: Horizontal Cleanout
Forum Title Date
Plumbing Forum, Professional & DIY Advice Vertical to Horizontal/Cleanout? Nov 30, 2016
Plumbing Forum, Professional & DIY Advice Would appreciate a review of my plumbing layout and esp. cleanout on horizontal runs Mar 8, 2016
Plumbing Forum, Professional & DIY Advice Toilets, horizontal wet vents, and end of line cleanouts Jan 2, 2015
Plumbing Forum, Professional & DIY Advice Where does the cleanout for long trap arm continuing into horizontal drain go? Dec 31, 2014
Plumbing Forum, Professional & DIY Advice vertical-to-horizontal transition: long bend only or or Y plus 45 with cleanout? Jun 14, 2013

Share This Page