3 phase to 240

Users who are viewing this thread

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Depends...what are the actual supply's voltages? 3-phase tends to be with the phases 120-degrees out of phase, so if the WH doesn't have any electronics in it, it would depend on what voltage you actually develop between the two phases you choose. A heating element just cares about the voltage between the two ends. If that's matched to the supply, doesn't matter.

In a really large situation, that unbalanced load on the supply transformer might be an issue.
 

Reach4

Well-Known Member
Messages
38,858
Reaction score
4,428
Points
113
Location
IL
Was that 208 three phase?
Is it ok to use 3 phase to a standard 240 hotwater tank and cap the unused wire?
I presume 208. The Franklin AIM manual specifies to change out the start relay in their 3-wire pump boxes. I did not see that they say what to do for a 2-wire pump.

https://faradynemotors.com/faradyne-products/control-boxes says the same... special relay available.


Oops.. I was somehow thinking well pump.

They sell WH elements intended for 208 if you want faster heating.
 
Last edited:

Bannerman

Well-Known Member
Messages
4,826
Reaction score
785
Points
113
Location
Ontario, Canada
Assuming the voltage is 208 volts between any two phases, the water heater will receive 208 volts so the heating elements output will be roughly 13% lower and so the water will heat slower compared to when 240 volts is supplied.

As you will be using only 2-phases of 3, the remaining wire will need to be capped.

With 3-phase, best if power usage is as equal (balanced) as possible across all 3-phases. Perhaps the phase that remains unused for water heating, can supply another high consumption heating device somewhere else in the home?
 

wwhitney

In the Trades
Messages
6,557
Reaction score
1,841
Points
113
Location
Berkeley, CA
If you run a resistive heating element designed for 240V at only 208V, the current will also be 208/240 as much as designed, so the heat output will be (208/240)^2 = 75% of the design level.

Cheers, Wayne
 