20A vs 15A GFCI for Bathroom?

Users who are viewing this thread

Idoc4u

Member
Messages
95
Reaction score
0
Points
6
Location
Indiana
Do most recommend a 20A GFCI outlet in a bathroom as a result of the potential wattage used by hair dryers and other small electrical appliances that use a great deal of watts?

Thank you.
 

Jim Port

Electrical Contractor
Messages
156
Reaction score
0
Points
0
Location
Maryland
Website
www.manta.com
There is no need for a 20 amp slot GFI in a bathroom. You will not find appliances in a residential setting that need the T-slot. Even a 15 amp slot GFI is rated for 20 amp thru-put.
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
Do most recommend a 20A GFCI outlet in a bathroom as a result of the potential wattage used by hair dryers and other small electrical appliances that use a great deal of watts?

20 amp circuit (#12 wire), yes.

20 amp receptacle (the thing you plug the hair dryer into), no.
 