20 amp 240v continuous load calculations

Users who are viewing this thread

Chuck B

sea-bee
Messages
122
Reaction score
2
Points
18
Location
levering, michigan
I am installing three (3) digital wall heaters in my cottage on a 240v 20 amp circuit. My calculation at 80% is 3,840 Watts.

However my plan is to install (2) 1,600 volt and (1) 800 volt heaters (wall units with built in thermostats) which places me at 16.666 amps and a 4,000 watt draw on the 20-amp circuit.

It is likely all heaters would run simultaneously in my northern Michigan cottage.

Does the additional .6666 amps over the 80% 16 amp calculation present a safety or CB trip problem in practice.

Thanks.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
On items that can be expected to be on continually, generally, the 80% rule does apply. It's actually calling for the circuit to be 125% of the load if it could be continuous for 3 or more hours, which when you look at it another way, equals 80%.
 