2 wire romex

Users who are viewing this thread

Rayh78

Member
Messages
98
Reaction score
3
Points
8
Location
Colonial Heights, Virginia
So home has older 2 wire romex no ground. Seems easiest way is to run a separate ground wire to the outlets.
No holes to drill in crawlspace since existing holes can handle the one wire.

Is it worth the extra work to just go ahead and drill new holes and run new romex. But then would have the old wires just cut off in the wall and crawlspace. Dont think can pull them out being stapled to studs.

Any opinions?

Thanks
 

Reach4

Well-Known Member
Messages
38,862
Reaction score
4,430
Points
113
Location
IL
What is your objective? What you describe is not allowed by code, but it might help toward your objective. I am not an electrician, and an electrician is not going to approve that.

If your objective is to have 3-prong outlets, then there is an easy and permitted way: install 3-wire GFCI outlets, and label the outlets in a particular way.
 

Rayh78

Member
Messages
98
Reaction score
3
Points
8
Location
Colonial Heights, Virginia
What is your objective? What you describe is not allowed by code, but it might help toward your objective. I am not an electrician, and an electrician is not going to approve that.

If your objective is to have 3-prong outlets, then there is an easy and permitted way: install 3-wire GFCI outlets, and label the outlets in a particular way.

Yes, that is really my question. If it would meet code. So the ground wire cannot be separate from the romex.
 

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
Did you verify that there really is no ground wire? In the old days installers used to just cut it off as they didn't know what to do with it.

The easiest solution that is legal in most places is to leave things as is. If you want to clean things up a bit you can install new two prong receptacles as they are still sold in most of the big box stores.

Running a separate ground wire is to code for "Nongrounding Receptacle Replacement or Branch Circuit Extensions" as long as it goes back to the panel/GEC. It is rarely done as by the time you make room for another wire you could re-pull a new cable.
 

Reach4

Well-Known Member
Messages
38,862
Reaction score
4,430
Points
113
Location
IL
Running a separate ground wire is to code for "Nongrounding Receptacle Replacement or Branch Circuit Extensions" as long as it goes back to the panel/GEC.
I am glad I was wrong.
 

Rayh78

Member
Messages
98
Reaction score
3
Points
8
Location
Colonial Heights, Virginia
Did you verify that there really is no ground wire? In the old days installers used to just cut it off as they didn't know what to do with it.

The easiest solution that is legal in most places is to leave things as is. If you want to clean things up a bit you can install new two prong receptacles as they are still sold in most of the big box stores.

Running a separate ground wire is to code for "Nongrounding Receptacle Replacement or Branch Circuit Extensions" as long as it goes back to the panel/GEC. It is rarely done as by the time you make room for another wire you could re-pull a new cable.

That was exactly what I was considering. There is room to get a single green insulated 12g wire to force up thru the hole. But would have to drill holes to run one or two new 12-2 romex cables up to box. And then would look sloppy with just haveing to cut off the old romex below the floor.

Also did verify no ground. Just want to update the house.
 