2 inch vs 3 inch vent run

Skudbilt

New Member
Messages
4
Reaction score
0
Points
1
Location
New England
Hello-
I am updating a pair of adjacent bathrooms, and am hoping to vent with 2 inch as shown (step up to 3 in attic to exit through roof). Is this sufficient or should the vent in question be maintained at 3 inch all the way up? Single story home in Rhode Island. Thanks
 

Attachments

  • IMG_1044.jpeg
    IMG_1044.jpeg
    45.2 KB · Views: 112

Sylvan

Still learning
Messages
3,193
Reaction score
831
Points
113
Location
New York
I was stationed in Newport the last year of my enlistment and drive there several times a year.

Knowing how cold RI gets, I would go through the roof with 4" to prevent hoarfrost
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,902
Reaction score
518
Points
113
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
I was stationed in Newport the last year of my enlistment and drive there several times a year.

Knowing how cold RI gets, I would go through the roof with 4" to prevent hoarfrost

you have a good point, run a 2 inch vent up to the penetration through the roof and
then increase it to 4 inch........ we used to increase a 1 1/2 vent out the roof with a 3 inch increaser
and never had any issues
 

Sylvan

Still learning
Messages
3,193
Reaction score
831
Points
113
Location
New York
you have a good point, run a 2 inch vent up to the penetration through the roof and
then increase it to 4 inch........ we used to increase a 1 1/2 vent out the roof with a 3 inch increaser
and never had any issues

NYC always required a 4" penetration through the roof; even if the vent was 11/2" it had to be increased to 4" when going through the roof
 

Reach4

Well-Known Member
Messages
42,131
Reaction score
5,193
Points
113
Location
IL
https://codes.iccsafe.org/content/IPC2018/chapter-9-vents says

903.2Frost closure.​

Where the 97.5-percent value for outdoor design temperature is 0°F (-18°C) or less, vent extensions through a roof or wall shall be not less than 3 inches (76 mm) in diameter. Any increase in the size of the vent shall be made not less than 1 foot (305 mm) inside the thermal envelope of the building.
My point was that the increase should not be right below the roof if this is a really cold place. I doubt that NYC is that cold for this purpose.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,902
Reaction score
518
Points
113
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
https://codes.iccsafe.org/content/IPC2018/chapter-9-vents says


My point was that the increase should not be right below the roof if this is a really cold place. I doubt that NYC is that cold for this purpose.


Its never been a problem to throw a 36 inch piece of 3 inch PVC through the roof flashing with half above and half below in the attic then reduce it down to 2 inch or 1 1/2 it always works just fine and dandy

very , very rarely is this gonna freeze over ,
maybe during a polar vortex lasting a week or more. you might notice a sluggish drain
but its only gonna be temporary thing...

something like a fart in a breeze
 

Reach4

Well-Known Member
Messages
42,131
Reaction score
5,193
Points
113
Location
IL

Skudbilt

New Member
Messages
4
Reaction score
0
Points
1
Location
New England
Thanks everybody. Picked up a 4 inch flashing today. Looking forward to removing the old vent chase and getting some needed space back.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,902
Reaction score
518
Points
113
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
Thanks everybody. Picked up a 4 inch flashing today. Looking forward to removing the old vent chase and getting some needed space back.

I hope you got a short scrap of 4 inch PVC laying around..
they dont normally sell that stuff in 24 inches
so you will probably have to go buy a full 10 foot length

good luck and have fun
 

Reach4

Well-Known Member
Messages
42,131
Reaction score
5,193
Points
113
Location
IL
Home Depot offers 2 ft for about half of what 10 ft would cost.
If you buy the 10 ft and cut it, the remainder could be used potentially.

I use a piece of 4 inch to hold dowel rods, extra-long drill bits, and such.
 
Last edited:

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,902
Reaction score
518
Points
113
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
Home Depot offers 2 ft for about half of what 10 ft would cost.
If you buy the 10 ft and cut it, the remainder could be used potentially.

I use a piece of 4 inch to hold dowel rods, extra-long drill bits, and such.

Maybe you could sell it in your next garage sale too.... LOL
 

Sylvan

Still learning
Messages
3,193
Reaction score
831
Points
113
Location
New York
https://codes.iccsafe.org/content/IPC2018/chapter-9-vents says


My point was that the increase should not be right below the roof if this is a really cold place. I doubt that NYC is that cold for this purpose.
For several years, we had below-freezing temperatures for a week or more, which caused numerous no-heat calls

POI according to the old NYC code, PVC is not supposed to be exposed to direct sunlight, as it can become brittle and crack.
 

Reach4

Well-Known Member
Messages
42,131
Reaction score
5,193
Points
113
Location
IL
POI according to the old NYC code, PVC is not supposed to be exposed to direct sunlight, as it can become brittle and crack.
Good point. Ideal would be a lead flashing that covers the pipe. https://www.lowes.com/pl/roofing/flashings/vent-pipe-flashing/lead/4294524184-4294386969

Latex paint would be a good second-choice.https://www.charlottepipe.com/articles/combating-uv-degradation-in-plastic-piping-systems

If it were allowed, or if you don't care about the technical code violation, PVC electrical conduit would be good material to run up thru the roof. https://www.mcmaster.com/products/n...t-2~/rigid-pvc-conduit/?s=nonmetallic-conduit It is UV-resistant. The UV conduit is the same size as other PVC pipe, and glues into the same fittings.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,902
Reaction score
518
Points
113
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
For several years, we had below-freezing temperatures for a week or more, which caused numerous no-heat calls

POI according to the old NYC code, PVC is not supposed to be exposed to direct sunlight, as it can become brittle and crack.
LOL...PVC is exposed to sunlight on every rooftop around our state.......
Yes, It might get brittle over time but I doubt that anyone is going
to go up on that roof and smack it hard enough to crack it..... and even in sunlight
they claim its still good for 100 years anyway...... underground it is good for 500 years or more

Now, just for conversations sake on a sleepy Sunday afternoon....................................

I have encountered many a neoprene rubber flashing that was totally worn out after less than15 years
and they leaked through into the second floor ceilings when it rained hard .......
I Had to take tar patch and smear a load of it over a number of them due to the
roof being too brittle to replace the flashing without damaging the roof itself.......
Tar patch is good for another 30 years more or less..

I figure in 30 years I should be in the ground by then....:D:D
 

Sylvan

Still learning
Messages
3,193
Reaction score
831
Points
113
Location
New York
LOL...PVC is exposed to sunlight on every rooftop around our state.......
Yes, It might get brittle over time but I doubt that anyone is going
to go up on that roof and smack it hard enough to crack it..... and even in sunlight
they claim its still good for 100 years anyway...... underground it is good for 500 years or more

Now, just for conversations sake on a sleepy Sunday afternoon....................................

I have encountered many a neoprene rubber flashing that was totally worn out after less than15 years
and they leaked through into the second floor ceilings when it rained hard .......
I Had to take tar patch and smear a load of it over a number of them due to the
roof being too brittle to replace the flashing without damaging the roof itself.......
Tar patch is good for another 30 years more or less..

I figure in 30 years I should be in the ground by then....:D:D
I never said I agreed with some of the code officials; I just stated a fact.

Today, we live in a society that has found it is easier to win a lawsuit than buy a lottery ticket.


If a leak were to occur through a vent terminal, a plumber could argue that the PVC had become brittle and lost its integrity.

It was common to have a plumbing inspector fail the inspection with PVC exposed to direct sunlight, so to pass, plumbers would put NO HUB CI through the roof 2 feet above the roof for non-Promenade roofs and 7 feet high for Promenade roofs

When I installed a vent terminal, I used a caulked CI flange, and I have never seen one fail in over 57 years. Lead and okum is still the best way to ensure integrity

 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,902
Reaction score
518
Points
113
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
I never said I agreed with some of the code officials; I just stated a fact.

Today, we live in a society that has found it is easier to win a lawsuit than buy a lottery ticket.

If a leak were to occur through a vent terminal, a plumber could argue that the PVC had become brittle and lost its integrity.


It was common to have a plumbing inspector fail the inspection with PVC exposed to direct sunlight, so to pass, plumbers would put NO HUB CI through the roof 2 feet above the roof for non-Promenade roofs and 7 feet high for Promenade roofs

When I installed a vent terminal, I used a caulked CI flange, and I have never seen one fail in over 57 years. Lead and okum is still the best way to ensure integrity


People must be pretty nasty in New York City to sue over something like that
We never had anyone pull a stunt like this in our area......
I suppose throwing a peice of cast out the roof might be a good idea but why not just a
lead boot flashing??

when I was a kid I used to have the job of going up on the roof and installing a lead flashing on the 3 inch copper vents that
the guys installed...... the lead flashings are still working after 60 years in every home we did.....

I know the neopreme rubber ones are all going bad by now
but they were probably 1/5th the price of the old fashioned lead boots

not my problem any more
 

Sylvan

Still learning
Messages
3,193
Reaction score
831
Points
113
Location
New York
"I know the neopreme rubber ones are all going bad by now
but they were probably 1/5th the price of the old fashioned lead boots"

The cast Iron vent "boot" may cost 5 times, but they normally last over 50 years

If you're charging the right price, why not install better materials?

I did a job in 1963 when I was on a roof while helping my father.

The architect wanted a 50-year guarantee on the roof and was willing to pay for it

I used lead-coated copper and soldered the joints, and used Bronze roof drains, lead, and oakum joints

This roof will last well over 100 years
 
Top