Wayne it is only going be 120 only. Deep freeze etc. Some outlets and lights.thank youThat's the wrong wire for a standard 120/240V subpanel. You need 4 conductors--two hots, a neutral, and an EGC (which may be bare). You have only 3 conductors, two insulated and the segmented bare conductor, which can be the EGC. So you could use it for a 120V only subpanel, or a 240V subpanel, but not a 120/240V subpanel.
For a 120/240V 100A subpanel, I'd suggest 2-2-2-4 Al SER cable supplied by a 90A breaker, or 1-1-1-3 Al SER cable supplied by a 100A breaker.
To answer your question, the bare wire around the outside of the two insulated conductors is the third conductor, when you strip the outer sheath off, you can gather the exposed portion together and twist it into a bare stranded conductor.
Cheers, Wayne
OK, I take that to mean a detached garage, and that the PVC will be underground. Then a couple points:The main panel is in the house on outside wall. The sub panel will be in the garage 100 feet away from house.
It be in( pvc electric )conduit all the way.
The main panel is in the house on outside wall. The sub panel will be in the garage 100 feet away from house.
It be in( pvc electric )conduit all the way.
This is awkward, but...