Recommendations for proper way to install expansion tank with new water heater

Users who are viewing this thread

Messages
52
Reaction score
1
Points
8
Location
Atlanta GA metro area
Well, I live in a neighborhood about 15 years old. My next door neighbor's gas water heater just failed, as well as my neighbor across the street. Of course the builder didn't spend the extra nickel to put a pan and drain pipe under water heater so I am scared mine failing and damaging all kinds of stuff I have. I know how to sweat pipes and have actually installed a water heater in my old house, but haven't had to deal with expansion tanks, as they are new code requirement. So, I took a look at how my next door neighbor's water heater was installed by professional plumber. The plumber installed the expansion tank horizontally(tank horizontal attached to vertical pipe) which Watts literature says is okay - http://media.wattswater.com/2915054.pdf but only if you support the tank. He didn't, it is just hanging there screwed into T-fitting. I have 2 options to install expansion tank when I buy new water heater next week. If I install the expansion tank vertically, I would have to extend the cold water supply a few feet on the ceiling, and then drop it straight down and back to the water heater. Would that be the best way to install the expansion tank, or should I just install it horizontally? If I do install it horizontally, what is the proper way to brace the expansion tank, given that the support would have to come from the ceiling? The closest wall is a foot or so away and is concrete that I'd rather not tap into.

Thanks.
 

Attachments

  • expansion.jpg
    expansion.jpg
    35.5 KB · Views: 23,077

JohnjH2o1

Plumbing Contractor for 49 years
Messages
1,188
Reaction score
13
Points
38
Location
Florida
Install it vertically. When installed horizontally and the bladder fails the tank fills with water and becomes to heavy to support itself.

John
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
If you, or anyone else, installs an expansion tank horizontally, it MUST have a support of some kind fastened to the ceiling. The ONLY way to install it safely without a support is hanging downward from the pipe in a vertical orientation. If it is "upward" gravity will still try to break it off once it fills with water.

pex-bent-expansion.jpg
 
Last edited by a moderator:
Messages
52
Reaction score
1
Points
8
Location
Atlanta GA metro area
Thanks for the replies. I had another thought on installing the expansion tank. Is there any reason why I shouldn't install it in the supply line strapped to the ceiling, like just before the elbow that brings the supply line down to the hot water heater? I don't see anything that says how near the water heater the expansion tank needs to be, so if I installed in the supply line on ceiling it would be probably 5-6 feet from the water tank connection.
 

JohnjH2o1

Plumbing Contractor for 49 years
Messages
1,188
Reaction score
13
Points
38
Location
Florida
That is fine as long as it between the valve and the heater. You don't want to be able to isolate the tank from the heater by turning off the valve.

John
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
You could strap it (the easier way normally), or build a shelf to set it on. Water weighs about 8#/gallon, so when it eventually fails, that's probably in the order of 25# or so hanging there. If it is hanging down, you won't spill much when you unscrew it. Sitting horizontal, it will dump some water when you unscrew it.
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
If your pipes are a the ceiling and run across the floor joints, center the tank between joints and strap it to the joints on each side. Somewhat like your Plan B drawing except the tank would be at ceiling height. Plan A would require designing a platform or some kind of support to the tank. No point in doing that.
 
Messages
52
Reaction score
1
Points
8
Location
Atlanta GA metro area
I like the idea of just strapping it all to the ceiling joists. I'll put new shutoff valve just upstream of it too. I know it will be a bit awkward to get at the shutoff valve in this setup, but not like I need to get at the shutoff a bunch of times every year anyway! My wife thinks I am over engineering this and installing the expansion tank horizontally even if it failed and filled with water would be no big deal. That's probably true, but there must be a good reason why the manufacturer says don't do this unless supported properly.
 

JohnjH2o1

Plumbing Contractor for 49 years
Messages
1,188
Reaction score
13
Points
38
Location
Florida
The tanks are made of a light weight steel and can sear off at the point of connection when the bladder fails and the tank fills with water.

John
 
Messages
52
Reaction score
1
Points
8
Location
Atlanta GA metro area
New water heater in including expansion tank. Expansion tank seems to have resolved our issue when we initially turned on shower would be a big rush of water, and then it would settle down to static pressure. Thanks all!
 

TxFLSTC

New Member
Messages
1
Reaction score
0
Points
1
Location
Austin Texas
Technically, the tank can be installed anywhere in the house, but ideally it should be connected between the heater's water valve and the heater.

Most if the info on the web indicates that you can install
an expansion tank vertically up or down, or horizontally
sideways, or even on a 45 degree angle, anywhere on
the cold. While technically correct, it seems to me that
tank up, connection at the bottom, close to & above the
HWH intake would be best;
Water would drain out of the tank, eliminating or reducing stagnate water.
Semi stagnate water would go into HWH, hopefully sanitized, >140, not into cold drinking water.
Completely drain each time system de-pressurized = no stagnate water
Would still function if bladder broke.
Bladder could still be checked by de-pressurizing system, if tank psi holds bladder ok.
Would drain out when replacing = low weight.
Thoughts ?
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,537
Reaction score
357
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
Usually we will install them on the cold line going into the water heater...
its always best to figure out a good way to support them ... I prefer to use a tee on the top of the heater
and install the therm tank onto this fitting.... placing a support leg under the arm.... I really dont care for them
because the seem to become water logged before the water heater fails and are worthless.. No one checks them and maintains them ....

.
index.php
 

Attachments

  • 1514.jpg
    1514.jpg
    15.4 KB · Views: 41,446

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Whenever water is forced into the ET, whenever you later open a valve, the bladder in the tank pushes out that stored water, so it is exchanged on a regular basis regardless of orientation. Install it in any orientation the manufacturer allows, but also support it properly, as it will fill with water once the bladder fails and will become quite heavy. How long that is depends on a lot of factors such as the static pressure, the frequency of hot water use (how often the bladder stretches), and your water chemistry.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,537
Reaction score
357
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
Whenever water is forced into the ET, whenever you later open a valve, the bladder in the tank pushes out that stored water, so it is exchanged on a regular basis regardless of orientation. Install it in any orientation the manufacturer allows, but also support it properly, as it will fill with water once the bladder fails and will become quite heavy. How long that is depends on a lot of factors such as the static pressure, the frequency of hot water use (how often the bladder stretches), and your water chemistry.

have you ever had a 5 gallon thermal expansion tank filled with water fall and land on your foot??
They are quite heavy and come down like a ton of bricks.... normally you get a good bath when you cut one out of the system....
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
have you ever had a 5 gallon thermal expansion tank filled with water fall and land on your foot??
They are quite heavy and come down like a ton of bricks.... normally you get a good bath when you cut one out of the system....
They're only heavy when they fail! This is why they need to be properly supported. Under normal circumstances, if you've precharged it properly, they do not hold much water, and when they do (after a WH reheating cycle), when you open a valve to use hot water, that gets pushed out by the bladder for the most part. If the precharge equals the actual water pressure, the bladder will sit at its neutral point, and not be holding much of anything. When the heated water expands, it compresses the bladder, but if it is large relative to the amount of water, the pressure doesn't rise much at all. If it is undersized, or underinflated, you'll have lots more water in it most of the time, and stretch it further than design, decreasing both its effectiveness and life, and, have a larger pressure change in the process.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
I'm installing a tank on the wall with a specially designed clamp for the purpose. The tank will connect via a flexible line to the T on the line between the shutoff valve and the tank. I'm a litle confused over where I might need dielectric couplings, if at all. It's an electric WH, copper plumbing.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,537
Reaction score
357
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
They're only heavy when they fail! This is why they need to be properly supported. Under normal circumstances, if you've precharged it properly, they do not hold much water, and when they do (after a WH reheating cycle), when you open a valve to use hot water, that gets pushed out by the bladder for the most part. If the precharge equals the actual water pressure, the bladder will sit at its neutral point, and not be holding much of anything. When the heated water expands, it compresses the bladder, but if it is large relative to the amount of water, the pressure doesn't rise much at all. If it is undersized, or underinflated, you'll have lots more water in it most of the time, and stretch it further than design, decreasing both its effectiveness and life, and, have a larger pressure change in the process.

yes, ok ----very good ----- and thank you for the lecture.....
That was very instructional . ---- yes a good read....

now you try to catch one that needs to be changed that is hanging about 8 feet up in the air and is
old, rusty and totally waterlogged.....

This is mostly the case after its 10 to 15 years old.......
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
The question was what orientation works...not where it is best for servicing...yes, it's better to have it lower and hanging so you can change it without taking a bath, but you can drop it from any position/location. Not having to reach over your head is safer. But, it will work wherever.
 

Keith Briggs

New Member
Messages
1
Reaction score
0
Points
1
Location
Evergreen, CO Captain Cook, HI
My 90+ year old boiler plumber mounts them vertically with the connection at the bottom and his arguments mirror what TxFLSTC comments are above.
1. they last longer
2. when the bladder fails they still work.
3. they are lighter
4. he adds a valve on it so you can swap it without draining the system
5. being all air, they have a higher capacity for a given size.
6. less prone to rusting out (may be redundant with lasting longer).

I'm installing an identical configuration on my solar hot water line. System is basically a single zone boiler where the boiler is the sun.
 
Last edited: